Zero export limitation on SUN2000L inverters

Latest reply: Apr 23, 2020 17:53:00 2518 2 3 0 0

This document describe the steps needed to be follow in order to setup the zero export limitation on SUN2000L inverters.

This post was last edited by user_3293479 at 2019-02-08 16:14.

This article contains more resources

You need to log in to download or view. No account? Register

x

Hello, can you do this configuration using two or three inverters in the same installation?
thanks
View more
  • x
  • convention:

Confucius
Confucius Created Apr 30, 2020 18:23:08 (0) (0)
Hi, yes, you can make zero export limitation on both inverters, or just on two of them and the third one can export to grid.
I know cases in Australia where customer installed 2 x SUN2000L-5KTL inverters and one was set as Zero Export Limit and the second wan feed the energy (no limit) into the grid.  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.