Why Can eSight Still Receive Alarms After Alarm Masking Is Enabled on Device Por

Latest reply: Mar 26, 2016 18:50:35 1479 1 0 0 0
Why can eSight still receive alarms after alarm masking is enabled on device ports?

After you select Disable Alarm Reporting on the NE Manager, devices are disabled from reporting alarms.

eSight periodically polls port status of network-wide devices and automatically generates alarms when the port status changes. These alarms are also displayed in the current alarm list. As a result, an alarm exists in the current alarm list although a device does not report a port status change. If you require that the alarm not be displayed in the current alarm list, mask this alarm by setting masking rules on the Masking Rule page.
Choose Monitor > Fault Management > Alarm Settings from the main menu.
Choose Masking Rule in the navigation tree, and set alarm masking rules as required.

View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.