Issue Description

Customer reported a problem when he started massive migration of virtual machines from one datastore to some others in Vmware 5.5 after several hours some target datastores gone failed state and could not be mounted. Source and target datastores were located on the same OceanStor 5500 V3 system, but in different pools, source in SAS tier pool, target in NL-SAS tier pool.

Vmware datastores on OceanStor 5500 V3 became failed and can‘t be mounted-1088271-1

The same way LUN devices of failed datastores were visible in Vmware and all paths were active.

Vmware datastores on OceanStor 5500 V3 became failed and can‘t be mounted-1088271-2

Alarm Information
No Alarm Information present on storage device during this issue take place.




Handling Process

During analysis of issue several log messages helped to make right conclusion.

1. Back bad records presence in storage logVmware datastores on OceanStor 5500 V3 became failed and can‘t be mounted-1205557-1

2. Path flapping records in Vmware logsVmware datastores on OceanStor 5500 V3 became failed and can‘t be mounted-1205557-2

Root Cause

The problem is in OceanStor 5500 V3 software version compatibility problem with 4K sector disks, which is described in TT DTS2015091001112.

Trouble Ticket Number

DTS2015091001112

Symptom

When random small read and write I/Os are sent to a 4K-sector disk, services are occasionally interrupted when the stripe depth of the storage pool is greater than or equal to 128 KB.

Severity

Suggestion.

Root Cause

If the stripe depth of the storage pool is greater than or equal to 128 KB, and the upper-layer services are random small I/Os, the upper-layer module integrates the size of I/Os sent to the 4K-sector disk into the I/Os whose size is no more than that of the stripe depth of the storage pool. When the number of memory pages of an integrated I/O occasionally exceeds the maximum of an I/O on the lower-layer module, the lower-layer module splits the integrated I/Os. The size of the split child I/Os may not be a multiple of the size of I/Os accepted by the 4K-sector disk; therefore, read and write I/O fail, resulting in occasional service interruption.

Solution

When the lower-layer module splits the I/Os that are sent to the 4K-sector disk, the module checks the size of each child I/O when it is split. If the size of the split I/Os is not a multiple of that of the I/Os accepted by the 4K-sector disk, the lower-layer module adjusts the size of the child I/Os to be a multiple of the I/Os accepted by the 4K-sector disk, and continues splitting the remaining I/Os.

Impact

There is no impact on the system.

Customer target datastores were located in NL-SAS pool based on large 4K sector disks. Described compatibility problem led to service disruption for some datastore LUNs and impossibility to mount datastores.

Solution

First, check which LUNs are placed on 4K disks and affected by problem:

In Running data log, search Disk Sectorif 4160, it’s 4K-sector disk.Vmware datastores on OceanStor 5500 V3 became failed and can‘t be mounted-1205557-3

Then apply following plan to resolve the problem:

1. install patch V300R001C20SPH001

2. Recovery fault page:

Force to flash all LUNs. Developer:/> change lun_fault_page recover lun_id_list=<4K LUNs list>Vmware datastores on OceanStor 5500 V3 became failed and can‘t be mounted-1205557-4

 

Run this command for every 4K disk LUNs.

3. Use Oceanstor toolkit to make inspection.

4. Migrate VM and check if problem is resolved.

View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.