URGENT!! Zero export to the grid- impossible to achieve

Created: May 23, 2020 09:07:36Latest reply: May 25, 2020 11:00:36 584 12 0 0 0
  Rewarded HiCoins: 1 (problem resolved)

Hi guys,

We tried very hard to achieve zero export to the grid,but it seems to be impossible with Sun2000 inverters.

I am not sure if i am doing something wrong with the Dongle or Inverters settings . Please see attached files  to have a look on the settings and our system diagram .


Many Thanks

Attachment: You need to log in to download or view. No account? Register

Featured Answers

Recommended answer

BetterMing
Created May 23, 2020 09:58:28

Hello, dear.
The inverter is set with zero output limit, which requires the use of ammeter and smartlogger. No relationship with dongle settings.
View more
  • x
  • convention:

huawei_cy
huawei_cy Created May 23, 2020 10:28:46 (0) (0)
Hello Dear,
Huawei advised us to use only Smart Dongle. They said no smartlogger needed.  
BetterMing
BetterMing Reply huawei_cy  Created May 25, 2020 07:39:43 (0) (0)
The Smart Dongle function is only for communication. You can connect with your mobile phone via Smart Dongle and use the Fusionsolar APP in your mobile phone to set the zero export restriction.  
huawei_cy
huawei_cy Reply BetterMing  Created May 25, 2020 09:05:19 (0) (0)
i know dear, but why you said that smartlogger needed ?  
BetterMing
BetterMing Reply huawei_cy  Created May 25, 2020 09:13:17 (0) (0)
Since the attachment is being scanned, I cannot recognize your SUN2000 model. Without the use of smart recorder devices, only some small inverters can use the electrical expression to zero output limits.  
huawei_cy
huawei_cy Reply BetterMing  Created May 25, 2020 09:18:23 (0) (0)
hi! i am using Huawei Inverter SUN2000MA-20KTL-M0  
BetterMing
BetterMing Reply huawei_cy  Created May 25, 2020 09:23:04 (0) (0)
Yes, I ’m looking for a setup guide for related zero output. Please wait  
ing.westphal
ing.westphal Reply BetterMing  Created Jun 14, 2020 10:21:43 (0) (0)
Hello,
I installed fusion solar app on 12 june 2020.
-There is no option to change zero export in the app.
-no energy control tab

How can I set zero export on my sun2000l inverter?  
All Answers
Hello, dear!
It's nice to meet you in the community.
We're working on your problem. Please be patient.
View more
  • x
  • convention:

Hello, dear.
The inverter is set with zero output limit, which requires the use of ammeter and smartlogger. No relationship with dongle settings.
View more
  • x
  • convention:

huawei_cy
huawei_cy Created May 23, 2020 10:28:46 (0) (0)
Hello Dear,
Huawei advised us to use only Smart Dongle. They said no smartlogger needed.  
BetterMing
BetterMing Reply huawei_cy  Created May 25, 2020 07:39:43 (0) (0)
The Smart Dongle function is only for communication. You can connect with your mobile phone via Smart Dongle and use the Fusionsolar APP in your mobile phone to set the zero export restriction.  
huawei_cy
huawei_cy Reply BetterMing  Created May 25, 2020 09:05:19 (0) (0)
i know dear, but why you said that smartlogger needed ?  
BetterMing
BetterMing Reply huawei_cy  Created May 25, 2020 09:13:17 (0) (0)
Since the attachment is being scanned, I cannot recognize your SUN2000 model. Without the use of smart recorder devices, only some small inverters can use the electrical expression to zero output limits.  
huawei_cy
huawei_cy Reply BetterMing  Created May 25, 2020 09:18:23 (0) (0)
hi! i am using Huawei Inverter SUN2000MA-20KTL-M0  
BetterMing
BetterMing Reply huawei_cy  Created May 25, 2020 09:23:04 (0) (0)
Yes, I ’m looking for a setup guide for related zero output. Please wait  
ing.westphal
ing.westphal Reply BetterMing  Created Jun 14, 2020 10:21:43 (0) (0)
Hello,
I installed fusion solar app on 12 june 2020.
-There is no option to change zero export in the app.
-no energy control tab

How can I set zero export on my sun2000l inverter?  

An update about the problem .

I just found out, if two of the inverters are connected and working , the consumption is very unstable,so we have lot of export in the grid.
I turn off the cascaded inverter and connect all the 40kw panels on the 20kw inverter, and then , consumption is very stable and no output .

Hope this can help you to find the problem.

difference with 1 and 2 inverters


View more
  • x
  • convention:

BetterMing
BetterMing Created May 25, 2020 10:50:12 (0) (0)
The fluctuation of self-consumption is related to many parameters, and I cannot see the problem from the figure.  
Hello, huawei_cy.
We have reviewed your parameter settings and plans in detail. We did not find your error. We hope you can contact the photovoltaic team. Provide the SN number of your inverter, inverter log, SDlongle log. There will be professional engineers to provide you with technical services. https://solar.huawei.com/eu/Contact
Thanks for your question.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.