Got it

UPS2000-G Fault

Created: Mar 26, 2020 07:30:35Latest reply: Mar 26, 2020 08:20:44 635 9 0 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hi all,


I have a UPS2000-G-10KRTL. I turned the UPS on, it worked normally, but when I was trying to switch it off, I got the fault number 0158 (photo).

What does this fault mean? How can I shut down UPS in this case?


P.S

Text on photo 2: 

Shutting down

Invertor shutted down. Shutdown command cannot be executed.

Attachment: You need to log in to download or view. No account? Register

Featured Answers

Recommended answer

BetterMing
Created Mar 26, 2020 07:46:48

Hello, Eugene_1.
After viewing the photos, the indicator light shows that your UPS is not turned on and is operating in bypass mode. After the UPS is connected to the power, press and hold the start button 3-5S to start the UPS.
The following is the information about the alert for your reference.

0158-1 On bypass Alarm

Attribute

Alarm IDAlarm SeverityAlarm Type

0158-1

Minor

Environmental alarm

Impact on the System

If the bypass is abnormal, the UPS may power off.

Possible Causes

  • The inverter is not started.

  • The load power exceeds the rated inverter loading capability.

  • The inverter is faulty.

Procedure

  1. Check whether other alarms are raised. If other alarms are raised, clear them.

  2. If no alarm is raised, start the UPS manually.

Thanks!

View more
  • x
  • convention:

All Answers
Hello, Eugene_1.
It's nice to meet you in the community.
We're working on your problem. Please be patient.
View more
  • x
  • convention:

Hi,

Can't see the attachments.
View more
  • x
  • convention:

BetterMing
BetterMing Created Mar 26, 2020 07:50:26 (0) (0)
After the user uploads the attachment, it takes a while for the forum to perform a security scan, and it will not be displayed until the security is confirmed.  

Hello, Eugene_1.
After viewing the photos, the indicator light shows that your UPS is not turned on and is operating in bypass mode. After the UPS is connected to the power, press and hold the start button 3-5S to start the UPS.
The following is the information about the alert for your reference.

0158-1 On bypass Alarm

Attribute

Alarm IDAlarm SeverityAlarm Type

0158-1

Minor

Environmental alarm

Impact on the System

If the bypass is abnormal, the UPS may power off.

Possible Causes

  • The inverter is not started.

  • The load power exceeds the rated inverter loading capability.

  • The inverter is faulty.

Procedure

  1. Check whether other alarms are raised. If other alarms are raised, clear them.

  2. If no alarm is raised, start the UPS manually.

Thanks!

View more
  • x
  • convention:

Thanks for your answer!
But I mean that: 1) I turn UPS on 2) UPS works without  any problems in normal mode 3) when I'm trying to shut down UPS according to User manual 5.2.2 Shutting down the UPS 4) After 'Step 2' (according to User manual 5.2.2, page 77) I see fault 0158

View more
  • x
  • convention:

Posted by BetterMing at 2020-03-26 07:46 Hello, Eugene_1.After viewing the photos, the indicator light shows that your UPS is not turned on a ...
Thanks for your answer!
But I mean that: 1) I turn UPS on 2) UPS works without any problems in normal mode 3) when I'm trying to shut down UPS according to User manual 5.2.2 Shutting down the UPS 4) After 'Step 2' (according to User manual 5.2.2, page 77) I see fault 0158
View more
  • x
  • convention:

BetterMing
BetterMing Created Mar 26, 2020 08:15:08 (0) (0)
Do you want to shut down the UPS to no output state?  
Hi, Eugene_1.
The UPS cannot be turned off to no output state. After the inverter is turned off, it will automatically go to the bypass. In the bypass state, it can no longer be turned off.
Thanks!
View more
  • x
  • convention:

Eugene_1
Eugene_1 Created Mar 26, 2020 16:16:03 (0) (0)
Thank you!  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.