U2000, OSN6800, OSN8800 - OTUk, ODUk and Client does not alarm when a high order alarm happens on the OCh due to U2000 configuration

236 0 0 0 0

Hello everyone!

Today, I’d like to share a case.

 

Problem Description

 When troubleshooting a WDM issue that a high order alarm ocours on the fiber the OCh and the corresponding OTN levels
(OTU, ODUk and Client) should alarm too, showing that there is an alarm on the path, but this is not happening

1

Checking the picture above you can see that the fiber is alarmed 

Now lets see the trail alarms,

2


As you can see, the OCh is alarmed but the related OTU2, ODU2 and Client show no alarms.



When a high order alarm is generated on a fiber like MUT_LOS or OTUk_LOF the corresondenting OTU,
ODU and Client of the OCh should be alarmed too.

MUT_LOS -  This alarm indicates a loss of multiplexed signals. This alarm is generated
when the input multiplexed signals of the board are lost.


OTUk_LOF - The OTUk_LOF is an alarm indicating that the frame alignment signal (FAS) is abnormal.
This alarm occurs when the frame alignment processing is out of frame (OOF) in three consecutive milliseconds.

 

 

Problem Analysis

 When analysing the problem it was check that the related OTN level were not alarming properly on the U2000 NMS.

 

Root Cause

 

N/A

 

Solution Description

After Checking the issue with R&D it was asked to check the value of a field bDisplayServerTrailAlarm
on the File Nml_otn on server configurations.

The parameters follow the rules 
bDisplayServerTrailAlarm 0 - No alarm will be displayed on the related OTN Trails.
bDisplayServerTrailAlarm 1 - Alarm will be displayed  on the related OTN Trails.


To check the value perform the following:

1 - On the Client instalation path open "... \U2000\client\tools\usercfgtool"
2 - Open the File " usercfgtool.bat"
3 - You will face a similar screen

3

Ps:By default the password of user " sa" is " Changeme_123"

4 - Look for the field  bDisplayServerTrailAlarm and check if the values correspond to the actual desired parameters.

4


As you can see above the parameter of  bDisplayServerTrailAlarm is  0 so we need to chenge it to 1 to enable the alarms to be
shown on U2000, after change its necessary to restart the process Nml_otn by System Monitor.

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.