Troubleshooting the Grid Code Mismatch alarm

441 0 0 0 0

Possible Causes:

The grid code set on NetEco or FusionHome app is inconsistent with the local grid code.


Solution:

Check that the DC side of the SUN2000L is energized, and set the grid code to the local grid code.

The installer can set the grid code on NetEco, and the user can set it on the FusionHome app.


Installer: Set the grid code on NetEco to the local grid code.

Step 1 On the main menu, click Monitor.

Step 2 In the navigation tree on the left, select the target device.

Step 3 In the operation area, select the Settings tab.

The device information is displayed on the tab.

Step 4 Select the Grid Parameters tab.

Step 5 On the Grid code tab, set the grid code.

This article contains more resources

You need to log in to download or view. No account? Register

x

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.