eSight Cannot Receive Device Alarms

Network Topology

Physical Network Topology

Figure 1-1 Network where switch alarms cannot be displayed on eSight

094226tsc9pju46lc9jjqs.png

 

Fault Description

The eSight cannot receive alarms contains folloing  scenarios:

l   The eSight cannot receive the alarm information from all the devices.

l   The eSight cannot receive the alarm information from one specified device.

l   The eSight receive the specified alarm information from one specified device.

In other words, the information about the alarm raise or clear has existed in the switch's log, but not displayed on the eSight.

Troubleshooting Location

Troubleshooting Procedure

Step 1      Check if the eSight is started normally and whether the 162 port is occupied.

1.         Start eSight to check whether an error is reported.

2.         Run the netstat -aon command in the CLI to find the PID of UDP port 162. In this example, the PID of UDP port 162 is 1716.

3.         Check the process name of the PID in the Task Manager. If the name is not java, port 162 is being used by another software.

094246qjrkyuq523tlrkur.png

094246jy7o3ieyyyee55l5.png

094318h3jj0jvaa3y4k0jn.png

Solution: Uninstall the software that uses port 162.


Step 2      Check whether the operating system firewall is turned on.

Choose Control PanelSystem and SecurityWindows FirewallCustomize Settings.

094345jd20cf9mx4cedddk.png

Solution:

On Customize Settings, select Turn off Windows Firewall (not recommended) and click OK.

     Note:You are advised to turn on Windows firewall after troubleshooting is complete. Otherwise, the settings may cause information security risks.


Step 3      Check whether a firewall is deployed between the eSight server and devices.

If a firewall exists, check whether policies on the firewall permit pass of trap messages. The policies are as follows:

l   Enabled ports: 162 and 10162

l   Supported protocol: UDP


Step 4      Ping the eSight server IP address from a device to check whether the device can communicate with eSight.

Check method and solution:

l   If the ping fails, check the network between the device and eSight.

l   If the ping succeeds only when the vpn parameter is specified, configure the vpn parameter in the snmp target-host command.

l   If the ping succeeds only when the source address is specified, configure the trap source in the snmp-agent trap source command.


Step 5      Check whether alarm masking is enabled on eSight.

1.         Check the alarm masking rule on eSight.

On the main menu, choose MonitorFault ManagementAlarm Settings. On the Masking Rule page, check whether an alarm masking rule is set.

094353c72y2z***t7auyf4.png

2. Check masked alarms on eSight.

On the main menu, choose MonitorFault ManagementMasked Alarms.

Disable the alarm masking rule, and check whether devices can report alarms.

094400ew5agzk9maakmduu.png

3.         Check whether traps of the device are recognized as events and stored in the event list.

On the main menu, choose MonitorFault ManagementEvents.

094406kbxjjnj5jzc3xzc7.png


Step 6      Check the alarm configuration on the device.

Check method:

Run the display cur | inc snmp command on the device in the IP domain.

The following lists the commands on a Huawei AC6605 as an example. (For other models, see the corresponding product documentation.)

For SNMPv1/v2c, run the following commands:

l   snmp-agent local-engineid xxx

l   snmp-agent sys-info version all

l   snmp-agent community read public

l   snmp-agent community write private

l   snmp-agent mib-view included iso-view iso

l   snmp-agent target-host trap  address udp-domain xx.xx.xx.xx params securityname public v2c private xxx

Solution:

[SNMPv1/v2c] (All the following commands are mandatory.)

       snmp-agent sys-info version v1 v2c
       snmp-agent community write private mib-view View_ALL
       snmp-agent community read public mib-view View_ALL
       snmp-agent mib-view View_ALL include iso
       snmp-agent trap source MEth0/0/1
       snmp-agent trap enable
       snmp-agent target-host trap-hostname xyp address 10.137.241.114 udp-port 162 trap-paramsname xyp
       snmp-agent target-host trap-paramsname xyp v2c securityname public

Table 1-1 Parameter description

Parameter

Description

version

The SNMP version number must be the same   as that specified on eSight and the trap version number for the target-host   parameter on the device.

community write

The write community must be the same as   that specified on eSight.

community read

The read community must be the same as   that specified on eSight.

mib-view

This parameter must be configured next to   the read and write communities, and it must contain the complete ISO node: snmp-agent mib-view View_ALL include iso.

address

The address must be the eSight server IP   address. If not, the eSight server cannot receive alarms from devices.

udp-port

This parameter specifies the port used by   the eSight server to receive alarms. The value can be 162 or 10162.

trap source

This parameter specifies the source that   sends trap messages. The IP address of the source must be the same as the   device IP address added on eSight.

securityname

The security name must be the same as the   read community name.

snmp-agent sys-info version v3 For SNMPv3, run the following commands: 

        snmp-agent mib-view View_ALL include iso
        snmp-agent group v3 snmpv3usergroup privacy read-view View_ALL write-view View_ALL notify-view View_ALL
        snmp-agent usm-user v3 snmpv3user snmpv3usergroup authentication-mode md5 DCD56463205105262F43A56805AF04A0 privacy-mode          des56 DCD56463205105262F43A56805AF04A0
        snmp-agent target-host trap-hostname eSightServerIP address 10.137.240.91 udp-port 162 trap-paramsname trapv3param 
        snmp-agent target-host trap-paramsname trapv3param v3 securityname snmpv3user privacy private-netmanager
        snmp-agent trap source MEth0/0/1
        snmp-agent trap enable

Table 1-2 Parameter description

Parameter

Description

version

The SNMP version number must be the same   as that specified on eSight and the trap version number for the target-host   parameter on the device.

privacy

This parameter specifies whether   authentication and encryption are required for communication using SNMPv3.   The value Privacy indicates   authentication + encryption. The value Authentication   indicates authentication + non-encryption. The value must be the same as the   encryption mode for trap messages specified in the snmp target-host command.

read-view/ write-view/ notify-view

The three parameters are mandatory when   you define an SNMPv3 group on a device. You can run the snmp-agent mib-view View_ALL include iso command to specify the   complete ISO node. If they are not configured, the default read permission is   internet, and the device does not   have write and alarm reporting permission.

snmpv3user

The value of this parameter must be the   same as the security name specified on eSight and the value of the   securityname parameter next to target-host on the device.

authentication-mode

This parameter specifies an   authentication mode. The value must be the same as that specified on eSight.

privacy-mode

This parameter specifies a privacy mode.   The value must be the same as that specified on eSight.

address

The address must be the eSight server IP   address. If not, the eSight server cannot receive alarms from devices.

udp-port

This parameter specifies the port used by   the eSight server to receive alarms. The value can be 162 or 10162.

trap source

This parameter specifies the source that   sends trap messages. The IP address of the source must be the same as the   device IP address added on eSight.


Step 7      Clear the browser cache. 

If an alarm is displayed on the alarm list or NE Manager, but unavailable in the current or historical alarm list, check the alarm information in another browser or clear the browser cache.



Common Cause

l   The port mapping of the Linux server is incorrect.

l   Port 162 of the eSight server is in use.

l   The firewall function is enabled on the eSight server.

l   Devices are fault, or they cannot communicate with the eSight server.

l   Masking rules are created on eSight to mask specified alarms.

l   SNMP parameters on devices are incorrect or not proper.

l   The device is disabled from sending alarms of a specific type.

 


Its hard
View more
  • x
  • convention:

Its hard
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.