[Troubleshooting] 9 load shedding in HUPS-240VEBM, but there is no battery alarm on UPS2000

Latest reply: Mar 5, 2022 11:23:52 902 6 4 0 0

Hello everyone, today I will share a case with you -9 load shedding in HUPS-240VEBM, but there is no battery alarm on UPS2000. 

【Problem Description】

 A customer feeds back that his UPS has no battery alarm.

【Problem Analysis】

1. UPS

Measure the terminal of UPS to check whether the voltage is normal

If it is 0v, please check the battery pack and battery breaker.

155623qhstcb1xjtwoe1ll.png

Start the UPS by the battery

If we can start UPS, the battery pack is good. Then close the AC input breaker. The alarm will disappear.

If you can’t start UPS, there are some problems with the battery, please check the battery pack.

155623wl9xo5cmcm3a955a.png

155623tl4zi3kpjktaivh4.png

When UPS is working in normal mode, check whether the voltage of the battery is normal on the LCD

155624orsrry9v31z9mrlm.png

2. Battery pack

Measure the terminal of the battery pack to see whether the voltage is normal

If it is 0V, it means that the loop is a break.

155624cpzxa05x2xbzpff2.png

Open the battery pack. Please measure the fuse to see whether it is good or not

155625f30yz9vtmy2rp397.png

•Open the battery pack. Please measure the battery one by one, check whether each battery’s voltage is normal (around 12V)?

155625h201307f7fez60vf.png

Open the battery pack. Check the connection cable of the battery, whether it is loose or not? Find the position in which the cable is a break between batteries.

155626ddkzxggl5qwo769q.png

3. Battery breaker

•If there is a breaker between UPS and battery pack

•Check whether the breaker of battery is turned on

•When the breaker is turned on, measure the resistance of each line if the value is not0 Ω, the breaker is faulty, please replace it

【Root Cause】

The customer did feedback on the result of checking the battery packs after a long time. And we can't export the logs from UPS either. 

【Solution Description】

 1. Check the total voltage of the battery.

 2. Check the voltage of each battery, cable connection, and fuse board.

The post is synchronized to: uninterruptible power supply 2000/5000

Practical case, useful solution!
View more
  • x
  • convention:

Thanks for sharing
View more
  • x
  • convention:

Good and helpful
View more
  • x
  • convention:

interesting content.
View more
  • x
  • convention:

VinceD
VinceD Created Mar 5, 2022 09:16:08 (0) (0)
 
Thanks for sharing
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.