《TP483000D Telecom Power Installation Guide》 Issue 02 Date 2022-01-30
1. TP483000D Cabinet Configuration
AC cabinet: TPA38631B-N20C, TPA38401B-N20C1
Rectifier cabinet: TPR48202B-N20C5 , TPR48302B-N20C5
DC cabinet: TPD48202B-N20C1, TPD48302B-N20C1
Intelligent PDC: TPD48202B-N20C6
Lithium battery cabinet: TBC1000B-NDA1
Rectifier: R48100G1
2. Setting Master/Slave Server Parameters
NOTICE
● SMU V500R003C10SPC010 and later versions support parallel system. If the site software version does not support parallel system, contact Huawei technical support.
● If the power system is configured with only one rectifier cabinet and no lithium battery cabinet is configured you do not need to set master/slave parameters.
● If the power system is configured with only one rectifier cabinet and lithium battery cabinets, set the rectifier cabinet as the master and lithium battery cabinets as the slave.
● If the power system is configured with multiple rectifier cabinets, one rectifier cabinet needs to be configured as the master and other cabinets (including lithium battery cabinets) as slaves, regardless of whether lithium battery cabinets are configured.
● If multiple power systems are in the same LAN and each power system is used independently, you must change the parallel system parallel ID. (In the same LAN, the parallel IDs of the power systems that are used independently must be configured. Otherwise, communication fails.)




With preceding installation, cable connection, and settings, the TP483000D can be paralleled. The output current of the rectifiers in all rectifier cabinets is equalized. You can view the parallel status of the master and slave rectifiers cabinets on the LCD.