Time out when reading data over Modbus TCP

Created: Dec 7, 2021 16:33:02Latest reply: Dec 23, 2021 01:35:16 464 7 2 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hi,


I have three cascaded inverters SUN2000-2KTL-L1 and one DTSU666-H.

The Smart Dongle WLAN-FE is connected in the first inverter using an ethernet cable, configured to use Modbus TCP, restricted to the PC IP I am using, both are in the same subnet.

The firmwares used are:

- On SUN2000 Inverters: V200R001C00SPC115

- On Smart Dongle WLAN-FE: V100R001C00SPC124


The modbus cable is going from the DTSU666-H to the first inverter (the one with the smart dongle) on port 3(B2) and 4(A2) , from the first inverter port 1 and 2  to the second (1.2 too) and from the second (1,2) to the third (1,2).


I have a PC from where I try to read one register from the smart meter and one register from each inverter, one after the other with 2s interval.

My problem is that I have regular timeouts on these reads, sometimes it's not working during a few minutes and restart to work.


I did the settings on the inverter as describe in one of the forum article and I am (I think) using the correct firmwares so I dont know what I am doing wrong.


If someone has the experience quering multiple inverters, do you experience the same modbus timeout ? On my side, if I use a connection timeout of less than a second I can't really connect to the dongle.


One question I have is about the modbus line, do I have to place a termination resistor ?

If yes, were do I need one ? On the first inverter and the last one between port A1 and B1 ? Somewhere else ?

Which resistors value should I use ?


Thank you





Featured Answers

Best answer

Recommended answer

gzzz
Admin Created Dec 8, 2021 01:44:40

Hello, friend.

For details, see section "Connecting Signal Cables" in SUN2000-(2KTL-6KTL)-L1 User Manual. Checking Inverter Cascading Scenarios. Check whether the cables are correctly connected. If the cable connection and networking mode are correct and the problem persists, you need to seek the help of the PV center. You can send an email to the following address to describe your problem and attach your SN.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

fabiancrg
fabiancrg Created Dec 8, 2021 18:44:07 (0) (0)
I checked the connection, probably one of the connector was not set correctly, after checking everything it is much better, I still have a time out from time to time but nothing dramatic.
Thank you for the suggestion.  
gzzz
gzzz Reply fabiancrg  Created Dec 9, 2021 00:50:05 (0) (0)
Hello, friend.
You're welcome. That's what we should do. Thank you for your recognition of us.  
All Answers
Thanks for contacting the Huawei community!

We are checking your question and will provide an answer to you shortly...
View more
  • x
  • convention:

gzzz
gzzz Admin Created Dec 8, 2021 01:44:40

Hello, friend.

For details, see section "Connecting Signal Cables" in SUN2000-(2KTL-6KTL)-L1 User Manual. Checking Inverter Cascading Scenarios. Check whether the cables are correctly connected. If the cable connection and networking mode are correct and the problem persists, you need to seek the help of the PV center. You can send an email to the following address to describe your problem and attach your SN.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

fabiancrg
fabiancrg Created Dec 8, 2021 18:44:07 (0) (0)
I checked the connection, probably one of the connector was not set correctly, after checking everything it is much better, I still have a time out from time to time but nothing dramatic.
Thank you for the suggestion.  
gzzz
gzzz Reply fabiancrg  Created Dec 9, 2021 00:50:05 (0) (0)
Hello, friend.
You're welcome. That's what we should do. Thank you for your recognition of us.  
GOOD ANSWER
View more
  • x
  • convention:

I have + - this same problem, the first reading register is almost always in time-out also I foresee this one + wait of 100ms before remaking a second and if this one works then there is no more errors

I get best results not using the dongle, but boring 1 socket per inverter and keeping it open as the readings then hardly ever cause any problems.

If there is the slightest error, the socket is closed, delay 3 seconds, ping, socket opening and it restarts (therefore interrupted 5 sec max in total)

Tomorrow I will test if the problem exists in 117 because after upgrade I had no more reading of the values and no time so I came back in 115 while waiting.

-----

J'ai +- ce même probléme, la première lecture registre est quasi systématiquement en time-out aussi je prévois celui-ci + attente de 100ms avant de refaire une seconde et si celle-ci fonctionne il n'y a ensuite plus d'erreurs

J'obtiens de meilleurs résultats en n'utilisant pas le dongle, mais ennoubrant 1 socket par onduleur et le garder ouvert car les lectures ne provoquent alors presque jamais de problèmes.

Si il se passe la moindre erreur, le socket est fermé, delais 3 secondes, ping, ouverture socket et ça redémarre (donc interrompu 5 sec max au total)

Demain je testerai si le problème existe en 117 car apres upgrade je n'avais plus de lecture des valeurs et pas le temps donc je suis revenu en 115 en attendant.
View more
  • x
  • convention:

gzzz
gzzz Admin Created Dec 23, 2021 01:35:16

Posted by Verwau at 2021-12-23 00:38 I have + - this same problem, the first reading register is almost always in time-out also I foresee ...

Hello, friend.

For details, see section "Connecting Signal Cables" in SUN2000-(2KTL-6KTL)-L1 User Manual. Checking Inverter Cascading Scenarios. Check whether the cables are correctly connected. If the cable connection and networking mode are correct and the problem persists, you need to seek the help of the PV center. You can send an email to the following address to describe your problem and attach your SN.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.