Alarm Information
The customer reporte that he couldn't access to the management portal and he realized that all the VM's got down.
Handling Process
1.- Huawei analysis Procedure
1-1 The Network Topology Diagram

1.1.2 analysis on Storage
1.1.3.1 Check the system status
Login device manager, we found that the storage system enters minisystem mode

1.1.3.2 Check the minisystem reason
According to the information collected by Winscp, there’s dual controller reset log. And the minisystem mode is caused by the repeat controller reset.
Controller A:

Controller B:

1.1.3.3 Check the reset reason
On the storage, there is log show that the copy task queue is full.

Root Cause
Root Cause:When a storage array is processing a large number of data copy requests initiated by hosts, a request wait queue will be generated, when more than 16 VM clone or migration tasks are simultaneously implemented on the host side, the request wait queue will be full and there is a high probability that controllers reset.Solution
Ensure that the number of VM clone or migration tasks that are simultaneously implemented on the host side do not exceed 16.
Final solution:
Online install hotpatch: OceanStor S5500T V200R002C00SPH403Suggestions
Iinstall hotpatch: OceanStor S5500T V200R002C00SPH403