The box-type transformer measurement and control remote signaling point is incorrect.

Latest reply: Mar 12, 2021 12:43:44 138 1 2 0 0


1. Problem description: Recently, during communication commissioning in the solar-fishery hybrid project, the door opening signal of the high-voltage room and low-voltage room is displayed as "closed" on the SmartLogger, and "min" on the background vendor, and "min" on the PMA.

 

160929wldd46aadrf2pt2p.png

 

 

2. Onsite check: After the measurement and control configuration file is uploaded again, the two remote signaling points still do not correspond. Press the travel switch several times onsite. The signal points of the SmartLogger and the back-end are consistent.

160929rhc33fmw6ge86lyj.png164344d2blbwpkwgqcdbl1.png

 

3. Problem solving: The problem is caused by the measurement and control travel switch. The O&M personnel are instructed to manually press the switch for several times.

160930wphmnmdccep3cqxp.png

 

 

 

Good
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.