Got it

Surge Protector on a Fixed Huawei Switch

Created: Sep 11, 2021 14:24:24Latest reply: Sep 11, 2021 15:17:32 208 4 0 0 0
  Rewarded HiCoins: 0 (problem resolved)

When and How Should a Surge Protector Be Used on a Fixed Huawei Switch?


Featured Answers

Best answer

Recommended answer

DDSN
Admin Created Sep 11, 2021 15:17:32

Hi hemin88,

Common Causes of Lightning Strikes

  • Outdoor network cables or power cables are routed overhead.

  • The switch is deployed outdoors but is not properly grounded.


Damages Caused by Lightning Strikes

  • If power cables of a switch are routed overhead in an outdoor environment, lightning strikes may burn the power supplies.

  • If network cables of a switch are routed overhead in an outdoor environment, lightning strikes may burn network ports of the switch.

Most lightning damages occur because lightning-induced current surges generated on Ethernet cables or power cables enter switches through signal ports. If the lightning strike energy exceeds the protection specifications of switches, such lightning damages cannot be avoided using general equipment surge protection measures such as installing a lightning rod or grounding the chassis. Surge protectors are recommended to protect switches against lightning damages.


Surge Protector Use Precautions

Take the following precautions to protect a switch from lightning:

  • Ensure that the ground cable is connected to a ground bar or a ground point on the cabinet.

  • Avoid routing cables overhead in an outdoor environment. Bury cables underground or route them in steel tubes.

  • To protect network ports from lightning, use 8-line surge protectors (or Huawei certified 4-line surge protectors. Non-certified 4-line surge protectors may turn common-mode surges into differentiated mode due to defects in product designs, and cannot protect network ports effectively).

  • When installing a network port surge protector, connect the IN end to terminals and the OUT end to the network ports of the switch.


I hope it helps!


View more
  • x
  • convention:

hemin88
hemin88 Created Sep 11, 2021 19:21:02 (0) (0)
This helps a lot, thanks  
All Answers
gzzz
gzzz Admin Created Sep 11, 2021 14:24:46

Hello, dear!

It's nice to meet you in the community.

We're working on your problem. Just a moment, please.


View more
  • x
  • convention:

Diego.Silva
Diego.Silva MVE Author Created Sep 11, 2021 14:42:31

Hi my good friend,

Surge protectors can be used under the following conditions:

Service port surge protection:

  • If power and network cables of a switch need to be routed outdoors, bury them underground or put them in steel pipes to protect the switch from lightning strikes.

  • If the network ports on the S5720I-SI series switches are connected to devices on a street pole, no surge protector needs to be installed. If the network ports are connected to devices on a tower, a network port surge protector must be installed.

  • To protect network ports from lightning, use 8-line surge protectors or Huawei certified 4-line surge protectors. Connect the IN ports to terminals and the OUT ports to network ports of the switch.

  • If fiber reinforcing ribs are used, ensure that they are properly grounded to protect the switches from lightning.


Power supply surge protection


When installing the S5720I-SI series switches in outdoor cabinets, ensure that the following requirements are met:

  • AC switch:

    • If the 220 V mains supply is used, install a 20 kA surge protector between the power port of the switch and the mains.

    • If power is supplied by an isolated inverter near the outdoor cabinet, no surge protector needs to be installed between the power port of the switch and the inverter.

  • DC switch: An isolated power supply must be used and placed in the same outdoor cabinet as the switch. Surge protection is required for the power input of the outdoor cabinet. The surge protector, power supply, and switch must be equipotential. The outdoor cabinet must be properly grounded and the grounding impedance must be less than or equal to 10 ohms. If a DC switch is connected to the PAC-260WA-E or PAC240S56-CN power module that is powered by the 220 V mains, install a 20 kA surge protector between the power input port of the PAC-260WA-E or PAC240S56-CN and the mains.

I hope it helpful!



View more
  • x
  • convention:

DDSN
DDSN Admin Created Sep 11, 2021 15:17:32

Hi hemin88,

Common Causes of Lightning Strikes

  • Outdoor network cables or power cables are routed overhead.

  • The switch is deployed outdoors but is not properly grounded.


Damages Caused by Lightning Strikes

  • If power cables of a switch are routed overhead in an outdoor environment, lightning strikes may burn the power supplies.

  • If network cables of a switch are routed overhead in an outdoor environment, lightning strikes may burn network ports of the switch.

Most lightning damages occur because lightning-induced current surges generated on Ethernet cables or power cables enter switches through signal ports. If the lightning strike energy exceeds the protection specifications of switches, such lightning damages cannot be avoided using general equipment surge protection measures such as installing a lightning rod or grounding the chassis. Surge protectors are recommended to protect switches against lightning damages.


Surge Protector Use Precautions

Take the following precautions to protect a switch from lightning:

  • Ensure that the ground cable is connected to a ground bar or a ground point on the cabinet.

  • Avoid routing cables overhead in an outdoor environment. Bury cables underground or route them in steel tubes.

  • To protect network ports from lightning, use 8-line surge protectors (or Huawei certified 4-line surge protectors. Non-certified 4-line surge protectors may turn common-mode surges into differentiated mode due to defects in product designs, and cannot protect network ports effectively).

  • When installing a network port surge protector, connect the IN end to terminals and the OUT end to the network ports of the switch.


I hope it helps!


View more
  • x
  • convention:

hemin88
hemin88 Created Sep 11, 2021 19:21:02 (0) (0)
This helps a lot, thanks  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."