Hello,

i want to use 3  33KTL Inverter in my next pv system.

The real power and the reactive power and must be controlled via two 4-20ma signals. A gradual regulation (100% / 70%/ 30%/ 0%) is not sufficient.

Can this be done via the analog inputs of the smartlogger 3000a? It is not exactly in the user manual.

Or must an adam 4117 converter to RS485 be used?


Thanks for your help.


Andreas


Featured Answers

Recommended answer

BetterMing
Created Mar 11, 2020 00:54:43

Hello, Andreas_TB295.
A forum user has proposed a solution to the problem, You can refer:

I found the solution.

I'm using a small part of the DRM function to reduce the production to zero.

DRM

Just need to connect the 4-20mA grid operator signal to AI2 or AI3 or AI4 (AI1 only 0-10v, not 4-20mA!)

Under Settings => DRM, choose the connection port (AI2, AI3 or AI4) and configure the startup current range regarding the signal of your grid operator.

DRM1

In my case it was 17mA.

If the signal is upper 17mA, production is 100%

If the signal is under 17mA, production is reduced to zero !.

The idea now is asking Huawei to have the possibility to reduce the power smoothly regarding the value of the grid operator.

For example:

17mA: production at 75%

14mA: production at 50%

10mA: production at 25%

under 7mA production 0%

Today with the DRM function and only 4-20mA signal, we can't reduce smoothly the production without using DI inputs.

Thanks!

View more
  • x
  • convention:

All Answers

Hello, Andreas_TB295.
A forum user has proposed a solution to the problem, You can refer:

I found the solution.

I'm using a small part of the DRM function to reduce the production to zero.

DRM

Just need to connect the 4-20mA grid operator signal to AI2 or AI3 or AI4 (AI1 only 0-10v, not 4-20mA!)

Under Settings => DRM, choose the connection port (AI2, AI3 or AI4) and configure the startup current range regarding the signal of your grid operator.

DRM1

In my case it was 17mA.

If the signal is upper 17mA, production is 100%

If the signal is under 17mA, production is reduced to zero !.

The idea now is asking Huawei to have the possibility to reduce the power smoothly regarding the value of the grid operator.

For example:

17mA: production at 75%

14mA: production at 50%

10mA: production at 25%

under 7mA production 0%

Today with the DRM function and only 4-20mA signal, we can't reduce smoothly the production without using DI inputs.

Thanks!

View more
  • x
  • convention:

I have already read this article.
The following problems are imho not solved:
- the reactive power cannot be controlled
- the real power can not be continuously adjusted (only in steps)

Can the real power and reactive power be provided via the Modbus (RS485)?
View more
  • x
  • convention:

BetterMing
BetterMing Created Mar 11, 2020 02:37:18 (0) (0)
Yes. You can refer this link: https://support.huawei.com/enterprise/en/doc/EDOC1100108365/dbc828d3/setting-active-power-control  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.