SUN2000 -10KTL-M1 - how much panels of 41,2 V (VMP) per PV input

Created: 3 days agoLatest reply: Apr 19, 2022 07:40:17 113 6 1 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hi,


I have a SUN2000 -10KTL-M1 and 38 solar panels strings divided in two strings of each 19 panels. The panel specs are:

  • Maximum Power (Pmax): 395 W

  • Maximum Power Current (Imp): 9,59 A

  • Maximum Power Voltage (Vmp): 41,2 V

  • Short Circuit Current (Isc): 10,07 A

  • Open Circuit Voltage (Voc): 49,7 V


My question: can I connect all 38 panels on this inverter (10KTL-M1) or not ? 

If I am calculating correctly per string there is 19x41,2V =782,8 V for each PV string input so together (PV1+PV2) this would be 1565,6 V. This would exceed the total of 1100 V. 

Is there a set max for DC input PV1 and PV2 seperately ? 

Featured Answers

Best answer

Recommended answer

Clearlove7
Admin Created 3 days ago

Hello, friend.

1. PV1 and PV2 belong to different MPPTs. The voltages between PV1 and PV2 do not affect each other.

2. Maximum PV input voltage. The open-circuit voltage needs to be calculated, that is, 19x49.7.

3. If the same MPPT has two PV input strings regardless of the inverter model, the two PV input strings are connected in parallel. Therefore, the voltages should be the same rather than the sum.

View more
  • x
  • convention:

Saqibaz
Saqibaz Created 2 days 07:40 (0) (0)
 
All Answers

Hello, dear!

It's nice to meet you in the community.

We're working on your problem. Just a moment, please.

View more
  • x
  • convention:

Hello, friend.

1. PV1 and PV2 belong to different MPPTs. The voltages between PV1 and PV2 do not affect each other.

2. Maximum PV input voltage. The open-circuit voltage needs to be calculated, that is, 19x49.7.

3. If the same MPPT has two PV input strings regardless of the inverter model, the two PV input strings are connected in parallel. Therefore, the voltages should be the same rather than the sum.

View more
  • x
  • convention:

Saqibaz
Saqibaz Created 2 days 07:40 (0) (0)
 
Thanks for the quick response.

So if I understand this correctly for the SUN2000-10KTL-M1 inverter there is a maximum input voltage of 1100V per MPPT. Correct ?
View more
  • x
  • convention:

Clearlove7
Clearlove7 Created 2 days 01:20 (0) (0)
Hello, friend.
Yes, the maximum input voltage of the SUN2000-10KTL-M1 is 1100 V.  
Good answer
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.