SUN2000 10KTL cascade connection

Created: Nov 22, 2021 10:40:01Latest reply: Nov 23, 2021 02:15:10 425 8 0 0 0
  HiCoins as reward: 0 (problem unresolved)

Hi,

we have installed 2 SUN2000 10KTL in cascade following the instruction manual with RS485 the slave and WiFi dongle to the master.

During the installation trough fusionsolar, everything went fine and it recognize both inverter and the dongle.

At the end of installation we only can see the master inverter in fusionsolar and non the slave.

We did not installed the power meter, is it compulsory to be installed?

Thanks for reply

Attachment: You need to log in to download or view. No account? Register

Featured Answers

Recommended answer

gzzz
Admin Created Nov 22, 2021 12:11:03

Hello, friend.

Yes, back current prevention requires a meter. Use a smart meter. The electric meter and the smart communication stick must be connected to the same inverter. If cascaded inverters are connected to energy storage devices, a maximum of three inverters can be cascaded, and any inverter can be connected to energy storage devices. (The inverter connected to the smart communication stick must be connected to the energy storage device.)

View more
  • x
  • convention:

conte71
conte71 Created Nov 22, 2021 12:36:35 (0) (0)
Many thanks for your reply:
- we do not have storage device installed
- Is the meter compulsory only to set the two inverter in cascade? We never had this condition using for i.e. Fronius or Kostal inverters setting in master and slave.
- Smart dongle is connected correctly at the moment to the master inverter
In case meter is a condition to operate in cascade, we may connect both inverters with it's dongle installed on each inverter and check them separately in fusion solar  
gzzz
gzzz Reply conte71  Created Nov 22, 2021 13:12:28 (0) (0)
Hello, friend.
Sorry, I didn't describe it clearly. The electric meter and energy storage are optional and not required. The electric meter is required only in the case of anti-backflow.  
conte71
conte71 Reply gzzz  Created Nov 22, 2021 14:20:48 (0) (0)
Ok thanks, may you tell me then what are we doing wrong with these PV System with 2 SUN2000 10KTL in cascade? We are able to see only one inverter in fusionsolar and the dongle, the second one (slave) has no dongle installed and is connected via RS485 to the master one. During the setup fusionsolar recognized both inverter and the dongle. I don't figure out what could be the issue.
Thanks.  
gzzz
gzzz Reply conte71  Created Nov 22, 2021 14:57:13 (0) (0)
Hello, friend.
The first of the two cases may be a problem with your device, please upgrade to the latest version. Secondly, it could also be a FusionSolar display error, we suggest you contact the PV center to deal with it. You can send an email to the following email address, describing your problem and attaching your SN number.
Europe Email: eu_inverter_support@huawei.com   
China and Asia Pacific: solarservice@huawei.com     
Latin America Email: la_inverter_support@huawei.com  
Tang_li
Tang_li Reply conte71  Created Nov 23, 2021 02:08:39 (0) (0)
Check whether the communication addresses and RS485 cables between the inverters are correct. (The two inverters must be unique.)  
All Answers
gzzz
gzzz Admin Created Nov 22, 2021 10:41:11

Hello, dear!

It's nice to meet you in the community.

We're working on your problem. Just a moment, please.

View more
  • x
  • convention:

gzzz
gzzz Admin Created Nov 22, 2021 12:11:03

Hello, friend.

Yes, back current prevention requires a meter. Use a smart meter. The electric meter and the smart communication stick must be connected to the same inverter. If cascaded inverters are connected to energy storage devices, a maximum of three inverters can be cascaded, and any inverter can be connected to energy storage devices. (The inverter connected to the smart communication stick must be connected to the energy storage device.)

View more
  • x
  • convention:

conte71
conte71 Created Nov 22, 2021 12:36:35 (0) (0)
Many thanks for your reply:
- we do not have storage device installed
- Is the meter compulsory only to set the two inverter in cascade? We never had this condition using for i.e. Fronius or Kostal inverters setting in master and slave.
- Smart dongle is connected correctly at the moment to the master inverter
In case meter is a condition to operate in cascade, we may connect both inverters with it's dongle installed on each inverter and check them separately in fusion solar  
gzzz
gzzz Reply conte71  Created Nov 22, 2021 13:12:28 (0) (0)
Hello, friend.
Sorry, I didn't describe it clearly. The electric meter and energy storage are optional and not required. The electric meter is required only in the case of anti-backflow.  
conte71
conte71 Reply gzzz  Created Nov 22, 2021 14:20:48 (0) (0)
Ok thanks, may you tell me then what are we doing wrong with these PV System with 2 SUN2000 10KTL in cascade? We are able to see only one inverter in fusionsolar and the dongle, the second one (slave) has no dongle installed and is connected via RS485 to the master one. During the setup fusionsolar recognized both inverter and the dongle. I don't figure out what could be the issue.
Thanks.  
gzzz
gzzz Reply conte71  Created Nov 22, 2021 14:57:13 (0) (0)
Hello, friend.
The first of the two cases may be a problem with your device, please upgrade to the latest version. Secondly, it could also be a FusionSolar display error, we suggest you contact the PV center to deal with it. You can send an email to the following email address, describing your problem and attaching your SN number.
Europe Email: eu_inverter_support@huawei.com   
China and Asia Pacific: solarservice@huawei.com     
Latin America Email: la_inverter_support@huawei.com  
Tang_li
Tang_li Reply conte71  Created Nov 23, 2021 02:08:39 (0) (0)
Check whether the communication addresses and RS485 cables between the inverters are correct. (The two inverters must be unique.)  

Check whether the communication addresses between the inverters (the two inverters must be unique) and the RS485 cable connections are correct.

In cascading scenarios, you need to manually search for cascaded inverters.

https://support.huawei.com/enterprise/en/doc/EDOC1100165056?section=o002


1


View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.