【Problem Description】

Some cameras connected to huawei switch can be powered on successfully and some cameras connected to huawei switch cannot be powered on.


【Problem Analysis】

                          Step 1     Huawei R&D and GTAC engineers conducted several tests and found that the problem.

On the Switch (TAISM-138A-CCTV-SW), GigabitEthernet0/0/1 and GigabitEthernet0/0/2 cannot be powered on, GigabitEthernet0/0/11 can be powered on successfully.


102653ucdjc1vnhvng7k67.png

                          Step 1     Through port cross-validation, it is found that the 11-port camera can be powered on when it is changed to port 0/0/1. the 1-port camera still cannot be powered on when it is changed to port 0/0/11

With this verification we confirm that there is a difference between the cameras

                          Step 2     The register is 0x73 when the camera is not powered on.0x73 means: classification overcurrent, the impedance detection result is too small



102713tnw4cwrieinwcfu8.png




102725gkvcbihlm84jdom8.png


102732q5whxp3hpahzvoex.png


                          Step 4    The process of powering on the phone by the PoE Switch includes: idle -> detection - > Classification - > power on, as shown in the following figure.

102802t1bh41m7gbg72lag.png


PoE power supply process

In summary, the reason why the 1-port camera cannot be powered on is the abnormality when the camera shakes hands with the switch.

                          Step 5   There are two possibilities for this situation: individual abnormality of camera and Switch detection signal is interfered.

                          Step 6     Typically, PoE switches use pairs 1/2 and 3/6 to power the camera, and pairs 4/5 and 7/8 are reserved, and we check that the camerathat can powered onport rate is FE. So we did one more testwe use one FE cable(that only have pairs 1/2 and 3/6)to connect the camera to the switch, and it can be powered on successfully



【Root Cause】

In summary, we analyzed that the reason of cameras (in TAISM-138A-CCTV-SW) cannot be powered on is that the switch detection signal is affected by the pairs 4/5 and 7/8 signal.

【Solution Description】


AConnect camera and switch with a FE network cable(The camera is a FE device)

BThe network cables on the switch side are re-crimped to FE.

CTo add the special jump cable and RJ45 connector between current cables and the camera, The special jump cable will only contain 1-2 and 3-6 pairs.

Note: The special jump cable can only be used for 100M Ethernet connection.

102846d823gysed18oecc2.png

A、Connect camera and switch with a FE network cable(The camera is a FE device)

B、The network cables on the switch side are re-crimped to FE.

C、To add the special jump cable and RJ45 connector between current cables and the camera, The special jump cable will only contain 1-2 and 3-6 pairs.

thanks for sharing
View more
  • x
  • convention:

the analysis step very complete
Step 1 Through port cross-validation, it is found that the 11-port camera can be powered on when it is changed to port 0/0/1. the 1-port camera still cannot be powered on when it is changed to port 0/0/11

With this verification we confirm that there is a difference between the cameras

Step 2 The register is 0x73 when the camera is not powered on.0x73 means: classification overcurrent, the impedance detection result is too small
View more
  • x
  • convention:

Typically, PoE switches use pairs 1/2 and 3/6 to power the camera, and pairs 4/5 and 7/8 are reserved, and we check that the camera(that can powered on)port rate is FE. So we did one more test:we use one FE cable(that only have pairs 1/2 and 3/6)to connect the camera to the switch, and it can be powered on successfully
View more
  • x
  • convention:

Connect camera and switch with a FE network cable(The camera is a FE device)

B、The network cables on the switch side are re-crimped to FE.

C、To add the special jump cable and RJ45 connector between current cables and the camera, The special jump cable will only contain 1-2 and 3-6 pairs.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.