Hi All,

My solar inverter keeps shutting down due to grid overvoltage alarm. I have read up forums and online articles and understand why this is occuring but I still have some doubts. Appreciate the experts here to share your opinion.


1. Lodged a complaint to installer. Installer keeps blaming grid overvoltage from energy distributor. No voltage rise calculation or troubleshooting done by installer so far. Installer increased sustain voltage threshold 10mins average from 255v to 258v within allowable limit and this reduces the shutdown occurrence but problem still occuring.


2. Lodged a complaint with energy distributor. Case under investigation. No ETA.


3. Inverter settings – 253v recovery start, 258v sustain voltage shutdown.

When inverter is shutdown after grid overvoltage (>258v) I quickly did a measurement on voltage at my house power socket using smart meter, it says 248v. This should be grid voltage as the inverter is already shut and keep looking for 253v and below to resume operations. After some time inverter came back online and could see Solar inverter FusionSolar app reporting 257v, and my home smart meter measurement around 256v. What I dont understand is why there is a difference on voltage captured by my smart meter 248v vs Inverter FusionSolar app 254v when Inverter is shutdown and waiting for grid connection. Sound like the inverter is seeing 6 to 8v higher than what is supplied by grid. I would assume if I am getting 248v at home socket then inverter should resume operation since threshold for recovery is 253v but it keeps waiting looking for grid connection, and FusionSolar App shows around 254v inverter output. 


What could be the problem here? 1) inverter, 2) installation and 3) grid?


FusionSolar

Smart Meter

Thanks


Featured Answers

Best answer

Recommended answer

BetterMing
Created Aug 16, 2020 12:16:02

Hello, Gred.
When the electricity generated by the power station cannot be consumed, it will increase the grid voltage. In addition, when measuring voltage, you should measure the output part of the inverter when an alarm occurs, instead of using a local socket. When the power station outputs energy, the voltage increases.
This is a problem with the grid and has nothing to do with the inverter.
View more
  • x
  • convention:

Gred
Gred Created Aug 17, 2020 15:27:38 (0) (0)
I agree with you, thank you. I did some testing when inverter is offline during night and can still see voltage at power socket ranging from 249v to 255v. Waiting energy provider to feedback investigation on grid overvoltage.  
All Answers
Dear friend!
Please rest assured that we'll be back with an answer shortly.
View more
  • x
  • convention:

Hello, Gred.
When the electricity generated by the power station cannot be consumed, it will increase the grid voltage. In addition, when measuring voltage, you should measure the output part of the inverter when an alarm occurs, instead of using a local socket. When the power station outputs energy, the voltage increases.
This is a problem with the grid and has nothing to do with the inverter.
View more
  • x
  • convention:

Gred
Gred Created Aug 17, 2020 15:27:38 (0) (0)
I agree with you, thank you. I did some testing when inverter is offline during night and can still see voltage at power socket ranging from 249v to 255v. Waiting energy provider to feedback investigation on grid overvoltage.  
When the SUN2000 is not connected to the power grid, the voltage is 248 V, which should be about 220 V. You need to find out why the voltage exceeds 28 V.
The SUN2000 startup protection must comply with the local grid code for grid connection,
View more
  • x
  • convention:

Gred
Gred Created Aug 17, 2020 15:26:28 (0) (0)
The standard here is 230v +10% -6% so 248v is normal.
Agree with BetterMing's answer above that measuring from power socket may not be accurate due to load in circuit. I have done a few more testing today with and without inverter online, and still getting fairly high voltage ranging from 249v to 255v even though inverter is offline. Already lodged a complaint with energy provider and awaiting inputs.  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.