Smartlogger 3000A power adjustment with 4-20mA grid operator signal

Created: Feb 17, 2020 13:30:18Latest reply: Feb 19, 2020 00:42:44 670 4 1 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hello,

I am using a Smartlogger 3000A connected to 7 inverters 60ktl.

The grid operator would like to adjust remotely the power of the inverterT by sending a 4-20mA signal to the smartlogger 3000A.

After reading the documentation, I think it's possible but not sure of the configuration steps to implement this.

Did you have a document explaining how to configure the power adjustment with a 4-20mA signal from the grid operator?

If signal is less than 17mA, it needs to cut off production. (Optionally, if signal is between 17 & 20 mA, we can reduce the production but not mandatory)

Thanks for your help.

Olivier

Featured Answers

Recommended answer

BetterMing
Created Feb 18, 2020 01:21:48

Hello, Eoxs.
I checked the user manual of smartlogger 3000A and it shows that only the AI interface supports 4-20mA signal input, but the AI port is used to receive the environmental monitor. And the access signal transmission distance does not exceed 10 meters. I will ask the relevant engineers if there is a way to achieve this.

Thanks.

View more
  • x
  • convention:

All Answers

Hello, Eoxs.
I checked the user manual of smartlogger 3000A and it shows that only the AI interface supports 4-20mA signal input, but the AI port is used to receive the environmental monitor. And the access signal transmission distance does not exceed 10 meters. I will ask the relevant engineers if there is a way to achieve this.

Thanks.

View more
  • x
  • convention:

Hello,

I found the solution.

I'm using a small part of the DRM fuction to reduce the production to zero.

DRM

Just need to connect the 4-20mA grid operator signal to AI2 or AI3 or AI4 (AI1 only 0-10v, not 4-20mA!)

Under Settings => DRM, choose the connection port (AI2, AI3 or AI4) and configure the startup current range regarding the signal of your grid operator.

DRM1

In my case it was 17mA.

If the signal is upper 17mA, production is 100%

If signal is under 17mA, production is reduce to zero !.

The idea now is asking Huawei to have the possiblility to reduce the power smoothly regarding the value of the grid operator.

For exemple:

17mA: production at 75%

14mA: production at 50%

10mA: production at 25%

under 7mA production 0%

Today with the DRM fuction and only 4-20mA signal, we canno't reduce smoothly the production without using DI inputs.

Is a developer reading this post ? i_f30.gif



View more
  • x
  • convention:

You can close the ticket !
View more
  • x
  • convention:

Posted by Eoxs at 2020-02-18 15:09 You can close the ticket !
Thank you for your sharing!
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.