Hello.

I have a question about Modbus TCP/IP interface for SmartLogger 2000: How can I read voltage and current PV parameters from inverter through SmartLogger? I browsed manual and finded 25 registers we can read, but where we can read PV parameters? Thank you. Best regards.

Featured Answers

Recommended answer

BetterMing
Created Feb 6, 2020 08:32:20

Hello, klima.

Please refer to the following information:

Connection Description 

The SmartLogger can be connected to the SUN2000 through an RS485 communications cable
or AC power cable. Communication modes for the SUN2000 with MBUS (PLC) and those
without MBUS (PLC) are different. Select an appropriate communication mode based on the
actual situation. 


For models with the MBUS (PLC) function, you can select either the MBUS (PLC) or RS485
communications mode. For models without the MBUS (PLC) function, you can select only
the RS485 communications mode. 


For the 1000 V SUN2000, the RS485 and MBUS (PLC) communication modes are mutually exclusive. 

  • If the RS485 communications mode is selected, do not connect an AC power cable to the MBUS
    (PLC) power input port of the SmartLogger.

  • If MBUS (PLC) is used, do not connect an RS485 communications cable.

For information about RS485 interface, you can refer to the following link: https://support.huawei.com/enterprise/en/doc/EDOC1100014379?idPath=22892350|21439560|7921563|21102414|21294677 (Article 4.5 in the article)

When you use the RS485 cable to connect the inverter to smartlogger2000, you can view the PV information in the WEB interface.

Thanks

View more
  • x
  • convention:

All Answers
Hello,
Please find below the answer
SmartLogger 2000-3215838-1
SmartLogger 2000-3215838-2
For more details : https://support.huawei.com/enterprise/en/doc/EDOC1100014379
Thanks
View more
  • x
  • convention:

Hello, klima.

Please refer to the following information:

Connection Description 

The SmartLogger can be connected to the SUN2000 through an RS485 communications cable
or AC power cable. Communication modes for the SUN2000 with MBUS (PLC) and those
without MBUS (PLC) are different. Select an appropriate communication mode based on the
actual situation. 


For models with the MBUS (PLC) function, you can select either the MBUS (PLC) or RS485
communications mode. For models without the MBUS (PLC) function, you can select only
the RS485 communications mode. 


For the 1000 V SUN2000, the RS485 and MBUS (PLC) communication modes are mutually exclusive. 

  • If the RS485 communications mode is selected, do not connect an AC power cable to the MBUS
    (PLC) power input port of the SmartLogger.

  • If MBUS (PLC) is used, do not connect an RS485 communications cable.

For information about RS485 interface, you can refer to the following link: https://support.huawei.com/enterprise/en/doc/EDOC1100014379?idPath=22892350|21439560|7921563|21102414|21294677 (Article 4.5 in the article)

When you use the RS485 cable to connect the inverter to smartlogger2000, you can view the PV information in the WEB interface.

Thanks

View more
  • x
  • convention:

@BetterMing We have MBus. RS485 not connected. We can see on smartlogger web link (IP web page) PV data, but I can't find register number for this data.

@wissal Link setting - unlimited.
View more
  • x
  • convention:

What is the model of the inverter?
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.