Single Phase BackupBox Off-grid load switch shutting off

Created: Dec 7, 2021 07:22:31Latest reply: Dec 8, 2021 15:09:12 268 5 0 0 0
  HiCoins as reward: 0 (problem unresolved)

Hi,


We have the following system designed:


5KTL-L1 + LUNA2000-5kW + DDSU-666H + Single Phase backup Box
Inverter Serial number - 1020B0079869

 

We have the following problem - the backup box off-grid load switch is constantly switching off. I think it has some relation to when the inverter starts to work in the morning. We think we have connected everything correctly, but it is our first BackupBox installation, so we cannot be sure 100%. I'm attaching a photo of the backup box connections.

The small white cable you see on 2 and 3 on the Grid blocks is the power supply for the smart meter.


Where should we look for the cause of the problem?


backupbox


Featured Answers

Recommended answer

gzzz
Admin Created Dec 7, 2021 09:26:18

Hello, friend.

According to your situation, you are advised to ask the PV center to help you locate the fault. You can send an email to the following email address to describe your problem and attach your SN.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

All Answers
Hi dear, we are working on it.
View more
  • x
  • convention:

gzzz
gzzz Admin Created Dec 7, 2021 09:26:18

Hello, friend.

According to your situation, you are advised to ask the PV center to help you locate the fault. You can send an email to the following email address to describe your problem and attach your SN.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

GOOD ANSWER
View more
  • x
  • convention:

Confucius
Confucius Moderator Created Dec 8, 2021 15:09:12

@Alexand3r, can't quite understand this: "The small white cable you see on 2 and 3 on the Grid blocks is the power supply for the smart meter".
What kind o power supply do you talking about? There is no such requirements for the DDSU666-H smart power sensor.
View more
  • x
  • convention:

user_4158877
user_4158877 Created Jan 25, 2022 04:42:12 (0) (0)
Smart power sensor needs voltage reference. Most installers conect L1 of the Smart power sensor after the ac breaker of the inverter in the main distribution panel , "same" point as input of "grid" in the backup box.
Please, indicate if this is something wrong or not recommended by Huawei. I notice it works the same as the connection point indicated in the UM diagrams, this means if there is an outage smart power sensor must turn off.
CTs must be connected in the right plac 

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.