I. Project Background
There is 612 inverter in this site, a totally 25 blocks with 25 STS, 25 SACU 2000D. Use third-party scada. our SACU will connect with the control room by the third-party switch which is configured by scada vendor.
II. Problem description
After connect all SACU to the control room and show up all information in scada interface, most of signal is ok. But when we on-grid and send the command to SACU, the connection become fail, after restart it will be connected and disconect after few minutes. The communication is not stable.
III. Fault locating and analysis:
Check whether of connection fiber cable.
Check whether configure of switch is used.
Check IP address is set in smartlogger, the IP map as below:
Sr. No. Description IP Address Description IP Address SMART TRANSFORMER 1 Smart Logger-1 192.168.8.150 SCADA SERVER-1 192.168.8.201 SMART TRANS-1 2 Smart Logger-2 192.168.8.151 SMART TRANS-2 3 Smart Logger-3 192.168.8.152 SMART TRANS-3 4 Smart Logger-4 192.168.8.153 SMART TRANS-4 5 Smart Logger-5 192.168.8.154 SMART TRANS-5 6 Smart Logger-6 192.168.8.155 SMART TRANS-6 7 Smart Logger-7 192.168.8.156 SMART TRANS-7 8 Smart Logger-8 192.168.8.157 SMART TRANS-8 9 Smart Logger-9 192.168.8.158 SMART TRANS-9 10 Smart Logger-10 192.168.8.159 SCADA SERVER-2 192.168.8.202 SMART TRANS-10 11 Smart Logger-11 192.168.8.160 SMART TRANS-11 12 Smart Logger-12 192.168.8.161 SMART TRANS-12 13 Smart Logger-13 192.168.8.162 SMART TRANS-13 14 Smart Logger-14 192.168.8.163 SMART TRANS-14 15 Smart Logger-15 192.168.8.164 SMART TRANS-15 16 Smart Logger-16 192.168.8.165 SMART TRANS-16 17 Smart Logger-17 192.168.8.166 SMART TRANS-17 18 Smart Logger-18 192.168.8.167 SCADA SERVER-3 192.168.8.203 SMART TRANS-18 19 Smart Logger-19 192.168.8.168 SMART TRANS-19 20 Smart Logger-20 192.168.8.169 SMART TRANS-20 21 Smart Logger-21 192.168.8.170 SMART TRANS-21 22 Smart Logger-22 192.168.8.171 SMART TRANS-22 23 Smart Logger-23 192.168.8.172 SMART TRANS-23 24 Smart Logger-24 192.168.8.173 SMART TRANS-24 25 Smart Logger-25 192.168.8.174 SMART TRANS-25 And found IP of smartlogger same layout with Lan port in smartlogger (default 192.168.8.10). So it will cause the connection will be lose with Lan and Wan port.

Solution:
Upgrade firmware of smartlogger to V300RC001SPC040 and then change IP of LAN port. (just version later than SPC040 can change mode or IP of LAN port).