I. Project Background

There is 612 inverter in this site, a totally 25 blocks with 25 STS, 25 SACU 2000D. Use third-party scada. our SACU will connect with the control room by the third-party switch which is configured by scada vendor.


II. Problem description

After connect all SACU to the control room and show up all information in scada interface, most of signal is ok. But when we on-grid and send the command to SACU, the connection become fail, after restart it will be connected and disconect after few minutes. The communication is not stable.


III. Fault locating and analysis:

  1. Check whether of connection fiber cable.

    Check whether configure of switch is used.

    Check IP address is set in smartlogger, the IP map as below:

    Sr. No.DescriptionIP AddressDescriptionIP AddressSMART   TRANSFORMER
    1Smart Logger-1192.168.8.150SCADA SERVER-1192.168.8.201SMART TRANS-1
    2Smart Logger-2192.168.8.151SMART TRANS-2
    3Smart Logger-3192.168.8.152SMART TRANS-3
    4Smart Logger-4192.168.8.153SMART TRANS-4
    5Smart Logger-5192.168.8.154SMART TRANS-5
    6Smart Logger-6192.168.8.155SMART TRANS-6
    7Smart Logger-7192.168.8.156SMART TRANS-7
    8Smart Logger-8192.168.8.157SMART TRANS-8
    9Smart Logger-9192.168.8.158SMART TRANS-9
    10Smart Logger-10192.168.8.159SCADA SERVER-2192.168.8.202SMART TRANS-10
    11Smart Logger-11192.168.8.160SMART TRANS-11
    12Smart Logger-12192.168.8.161SMART TRANS-12
    13Smart Logger-13192.168.8.162SMART TRANS-13
    14Smart Logger-14192.168.8.163SMART TRANS-14
    15Smart Logger-15192.168.8.164SMART TRANS-15
    16Smart Logger-16192.168.8.165SMART TRANS-16
    17Smart Logger-17192.168.8.166SMART TRANS-17
    18Smart Logger-18192.168.8.167SCADA SERVER-3192.168.8.203SMART TRANS-18
    19Smart Logger-19192.168.8.168SMART TRANS-19
    20Smart Logger-20192.168.8.169SMART TRANS-20
    21Smart Logger-21192.168.8.170SMART TRANS-21
    22Smart Logger-22192.168.8.171SMART TRANS-22
    23Smart Logger-23192.168.8.172SMART TRANS-23
    24Smart Logger-24192.168.8.173SMART TRANS-24
    25Smart Logger-25192.168.8.174SMART TRANS-25

    And found IP of smartlogger same layout with Lan port in smartlogger (default 192.168.8.10). So it will cause the connection will be lose with Lan and Wan port.


    IP address before upgrade  software smartlogger


    Solution: 

Upgrade firmware of smartlogger to V300RC001SPC040 and then change IP of LAN port. (just version later than SPC040 can change mode or IP of LAN port).

  1. upgrade software SPC040

  2. change IP address of LAN port

black queen


Good table information
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.