【Problem Description】:


A server cannot be powered on, with the following error message recorded in the SEL.

153508uns3fexi3x6cfxp6.png?A-1_2_en-us_i


【Problem Analysis】:


According to maintenance.log, the faulty circuit is CPU34_vmse.

153800ouns7ssqq0scsxsx.png?5.PNG

According to the circuit diagram, the circuit is on the mainboard and provides power for CPUs 3 and 4

153912axgxcuu14wwg94gw.png?6.PNG

Replace the mainboard. If the problem persists, check CPUs 3 and 4.


【Solution Description】:


Check the mainboard first and then CPUs 3 and 4. If "CPU12_vmse" is displayed, check the mainboard first and then CPUs 1 and 2.


【Experience】:


The hddbkp_vcc error in maintenance.log is a false error.

154203hx7cax9ag747babp.png?7.PNG

To determine whether it is a false error, check the drive backplane type. The backplane at the customer site is an 8-bay backplane. If it is a 25-bay backplane, determine the cause of the error.

155642azmmtthhtpa6uha5.png?A-1_2_en-us_i

  • x
  • convention:

Comment

Reply
You need to log in to reply to the post Login | Register

Notice Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " Privacy."
If the attachment button is not available, update the Adobe Flash Player to the latest version!
Login and enjoy all the member benefits

Login and enjoy all the member benefits

Login