Hello, i have this issue, my inverter is shutting down and at my chart appear 0 production.

Beside this, I encounter several errors, as in the attached picture.

Can someone tell me what to do?



This article contains more resources

You need to log in to download or view. No account? Register

x

Hello, friend.

1. Alarm ID2034 indicates that the power grid is overvoltage, the power grid voltage is higher than the allowed range, or the duration of the high voltage exceeds the high voltage crossing threshold.

Solution

  • If the fault occurs occasionally, the power grid may be abnormal for a short time. After detecting that the power grid is normal, the inverter recovers to normal operation without manual intervention.

  • If this problem occurs frequently, check whether the power grid voltage is within the allowed range. If not, contact the local power operator. If yes, change the power grid overvoltage protection threshold on the mobile phone app, SmartLogger, or NMS after obtaining the consent of the local power operator.

  • Check whether the peak voltage of the power grid is too high. If the fault occurs frequently and cannot be rectified for a long time, contact the power grid operator.

2. Alarm ID2039 indicates that the output overcurrent causes the power grid voltage to drop sharply or is short-circuited. As a result, the instantaneous output current of the inverter is excessively high and protection is triggered.

Solution

  • The SUN2000 monitors external operating conditions in real-time. After the fault is rectified, the SUN2000 recovers to normal operation without manual intervention.

  • If this alarm occurs frequently and affects the normal power generation of the plant, check whether the output is short-circuited.

3. Alarm ID2040 indicates that the DC component of the output current exceeds the allowed range.

Solution

  • The SUN2000 monitors external operating conditions in real-time. After the fault is rectified, the SUN2000 recovers to normal operation without manual intervention.

  • If the fault occurs frequently, contact the PV center to locate the fault. Send an email to the following email address describing your problem and attach your device's SN number.

Europe Email: eu_inverter_support@huawei.com    

China and Asia Pacific: solarservice@huawei.com     

Latin America Email: la_inverter_support@huawei.com 

View more
  • x
  • convention:

Saqibaz
Saqibaz Created 4 days ago (0) (0)
 
@K1du for that Grid Overcurrent alarm, please try to change the grid code or check what grid code you have there if you're staying in Australia.
For grid overvoltage alarms, you can check what is the maximum grid voltage recorded by the inverter and then to increase the protections with few volts over (from 253V as an example to 255V or 258V).
View more
  • x
  • convention:

Saqibaz
Saqibaz Created 4 days ago (0) (0)
 

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.