Hello, Community!
This post relates to the most common PPPoE Dialup Fails. Please have a read below.
1. Common Causes
The application of PPPoE involves PPPoE client and PPPoE server.
This fault is commonly caused by one of the following:
The interface configuration is incorrect.
The physical interface frequently alternates between Up and Down states.
User authentication fails.
No IP address is assigned to the PPPoE client.
No echo message is received.
2. Troubleshooting Flowchart
Figure 1-1 shows the troubleshooting flowchart.
Figure 1-1 Troubleshooting flowchart for failed PPPoE dialup
![]()
3. Troubleshooting Procedure
Saving the results of each troubleshooting step is recommended. If troubleshooting fails to correct the fault, you will have a record of your actions to provide Huawei technical support personnel.
Procedure
Step 1 Check that the physical interface is working properly.
Run the display this interface command on the physical interface to check whether the physical interface frequently alternates between Up and Down states.
If the physical interface frequently alternates between Up and Down states, check the physical connection or replace the cable.
If the physical interface is working properly, go to step 2.
Step 2 Check that the configuration is correct.
On the PPPoE server, check the configurations of the virtual template interface and Ethernet physical interface. On the PPPoE client, check the configurations of the dialer interface and Ethernet physical interface. Run the display this command in the interface view to check the interface configuration.
On the PPPoE server:
[Huawei-A-Virtual-Template10]display
this
ppp authentication-mode chap
[Huawei-A-aaa]display
this
local-user ub password cipher %$%$yYr|IcpfX4V8pb$"ueOS%>5,%$%$
On the PPPoE client:
[Huawei-B-Dialer10]display
this
ppp chap user
ub
ppp chap password simple ub
dialer-group
5
[Huawei-B-GigabitEthernet0/0/1]display
this
pppoe-client dial-bundle-number 10
[Huawei-B-dialer-rule]display
this
dialer-rule
dialer-rule 5 ip permit
If authentication is configured on the PPPoE server, check whether the user name and password are correctly configured on the PPPoE client. If the dial-on-demand function is configured on the PPPoE client, the PPP link is torn down when there is no traffic to be transmitted. Ensure that the dialer-rule-number value in the dialer-rule command is the same as the group-number value in the dialer-group command.
If the preceding configurations are all correct but the fault persists, go to step 3.
Step 3 Find out the dial-in failure cause.
On the PPPoE client, check whether the PPP protocol frequently alternates between Up and Down states because authentication fails. Run the following commands to check the displayed information. The dialer interface is the dialup interface of the PPP connection.
<Huawei-B>terminal
monitor
Info: Current terminal monitor is on.
<Huawei-B>terminal
debugging
Info: Current terminal debugging is on.
Info: Current terminal monitor is on.
<Huawei-B>debugging ppp all interface Dialer
10
If the following information is displayed, authentication fails.
<Huawei-B>Jan 21 2008 17:40:56.420.1+08:00
AR1220-B
MID_PPP/7/debug2:
PPP
Packet:
Dialer10:0 Input CHAP(c223) Pkt, Len
33
State SendResponse, code FAILURE(04), id 2, len
29
Message: Illegal User or password.
<Huawei-B>Jan 21 2008 17:42:37.520.4+08:00
AR1220-B
MID_PPP/7/debug2:
PPP
Packet:
Dialer10:0 Output LCP(c021) Pkt, Len
13
State reqsent, code ConfRej(04), id 1, len
9
AuthProto(3), len 5, CHAP
c22305
<Huawei-B>Jan 21 2008 17:42:37.530.6+08:00
AR1220-B
MID_PPP/7/debug2:
PPP
Packet:
Dialer10:0 Input LCP(c021) Pkt, Len
8
State opened, code TermReq(05), id 3, len
4
In the preceding command output, the first part of information indicates that a CHAP user name is configured on the PPPoE client and the PPP client receives a Challenge message from the PPPoE server and replies with a Response message. Because the CHAP password is incorrect or the user name or password does not exist, the PPPoE server sends a Response Failed message to the PPPoE client. The second part of the information indicates that no authentication information is configured on the PPPoE client or the authentication mode configured on the PPPoE client is different from that configured on the PPPoE server so the client refuses the authentication request from the server in LCP negotiation. If the client fails to be authenticated four times, the third part of the information is displayed, indicating that the PPPoE server sends a request to tear down the PPP connection between the server and client.
If authentication fails, check the authentication configuration and configure correct authentication user name and password for the PPPoE client.
If authentication succeeds but the fault persists, go to step 4.
Step 4 Check that an IP address is correctly assigned to the PPPoE client.
If an IP address is incorrectly assigned to the PPPoE client, check the related configuration of the PPPoE server. If IP addresses are assigned to the PPPoE client from a remote IP address pool, check whether there are available IP addresses in the remote IP address pool. Log in to the PPPoE server and run the following command to check the IP address pool.
[Huawei-A-ip-pool-mypoo]display ip pool name
mypool
Pool-name :
mypool
Pool-No :
0
Lease : 1 Days 0
Hours 0
Minutes
Domain-name :
-
DNS-server0 :
-
NBNS-server0 :
-
Netbios-type :
-
Position :
Local
Status :
Unlocked
Gateway-0 :
20.1.1.1
Mask :
255.255.255.0
VPN instance :
--
-----------------------------------------------------------------------------
Start
End Total Used Idle(Expired)
Conflict Disable
-----------------------------------------------------------------------------
20.1.1.1
20.1.1.254 253 1
252
0
0 0
-----------------------------------------------------------------------------
If the Idle field is displayed as 0, there are no available IP addresses. Use an IP address pool with available IP addresses instead of the IP address pool configured on the virtual template interface of the PPPoE server. If the negotiated IP address of the PPPoE client conflicts with another local IP address, the PPP protocol also frequently alternates between Up and Down states.
If the PPPoE server fails to assign IP addresses to the PPPoE client, check the IP address pool usage and use another IP address pool.
If the PPPoE server correctly assigns IP addresses to the PPPoE client, go to step 5.
Step 5 Check whether the PPPoE client correctly receives heartbeat messages.
Log in to the PPPoE client and run the following commands to check the command output.
<Huawei-B>terminal
monitor
Info: Current terminal monitor is on.
<Huawei-B>terminal
debugging
Info: Current terminal debugging is on.
<Huawei-B>debugging ppp lcp all interface Dialer
10
If outgoing Echo Request messages are displayed but no incoming Echo Reply message is displayed, the client cannot receive heartbeat messages.
[Huawei-B]
Jan 21 2008 19:20:37.790.2+08:00 AR1220-B
MID_PPP/7/debug2:
PPP
Packet:
Dialer10:0 Output LCP(c021) Pkt, Len
12
State opened, code EchoRequest(09), id c0, len
8
Magic Number
0560b017
If the client does not receive any response to its consecutive four heartbeat messages, it tears down the link with the server. If the client has received heartbeat messages but the fault persists, go to step 6.
Step 6 Collect the following information and contact technical support personnel.
Results of the preceding troubleshooting procedure
Configuration files, log files, and alarm files of the device
----End
This is my solution, how about you? Go ahead and share it with us!