Checking Before Power-On:
-The inverter is installed correctly and securely.
-Check that the DC switches and downstream AC output switch are OFF.
-Ground cables are connected securely, without open circuits or short circuits.
-AC output power cables are connected correctly and securely, without open circuits or short circuits.
-DC input power cables are connected correctly and securely, without open circuits or short circuits.
-The communications cables are connected correctly and securely.
-All the used connectors at the chassis bottom are sealed.
-The AC terminal cover is reinstalled.
-The maintenance compartment door is closed and the door screws are tightened.
-Idle DC input terminals are sealed.
-The idle USB port is plugged with a waterproof plug.
-Idle AC OUTPUT and COM connectors are plugged and the locking caps are tightened.
Powering On the SUN2000:
Before turning on the AC switch between the inverter and the power grid, use a multimeter to check that the AC voltage is within the specified range.
Procedure
Step 1 Turn on the AC switch between the inverter and the power grid.
Step 2 Turn on the DC switches at the bottom of the inverter chassis.
Step 3 (Optional) Measure the temperatures at the joints between DC terminals and connectors using a point-test thermometer.
To ensure that the DC terminals are in good contact, check the temperatures at the joints between DC terminals and connectors after the SUN2000 has been running for a period of time. Ensure that the temperature rise does not exceed 40°C.
Step 4 Connect with SUN2000APP as advanced user and check the inverter status
Login as Advanced user with SUN2000APPàRunning InfoàDetailsàCheck the inverter status
Powering Off the SUN2000
After the SUN2000 powers off, the remaining electricity and heat may still cause electric shocks and body burns. Therefore, put on protective gloves and begin servicing the SUN2000 five minutes after the power-off.
Procedure
Step 1 Run a shutdown command on the SUN2000 APP
Login as Advanced user with SUN2000APPàMaintenanceàPower off
Step 2 Turn off the AC switch between the SUN2000 and the power grid.
Step 3 Set the two DC switches to OFF.
Huawei Enterprise Technical Assistant Center will assist you 24x7
E-mail: eu_inverter_support@huawei.com
24*7 Hotline:
Europe +80 03 38 88 888 (except below countries):
Croatia/Latvia/Bulgaria +80 07 77 78 899
Iceland 800201866 Slovakia +40 31 22 61 915 Moldova 080061466
Serbia 800190899 Lithuania 880031499 Romania 0800400897
Australia 1800046639 Canada +40 31 22 61 915 New Zealand 080061466
America 1 877 9huawei
Link: http://solar.huawei.com/