PLC communication - Smartlogger cannot detect the inverters

419 0 0 0 1

After physically connecting Smartlogger and the inverters, the next step is to upload the SN list which contains all the serial numbers of the inveters connected into Smartlogger.


032815nbq33ujevyze43uy.png?Capture3.PNG


Some customers encountered the issue at this step. After the list is imported and Auto Assign Address is performed, Smartlogger is unable to detect the inverters.


033429g4kgq5642p0i4i82.png?Capture4.PNG


Solution


Before inserting the SN list, please make sure that the Anti-crosstalk is set on Disabled. Once you insert the SN list, the anti-crosstalk option will change by itself to Enabled.


034258dqylyeqzelr6urql.png?Capture5.PNG


Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.