Please connect locally to your inverter (as an Installer) and then change it from General-EN50549-LV to General-IEC61727.
Then you can monitor it for few days to see how it behaves. Anyway, since 26/02/2021 13:13:19, it stopped to report any Output Overcurrent alarm.
Also, started with 28 Feb 2021, inverter had some DC Arc Fault alarms on string No.2, if still persist please ask the installer to check the installation on the DC side (both strings) to be sure that there is no problem (faulty DC cable, connector, water ingress etc).
Waiting your feedback!