Output Overcurrent alarm id 2039

Created: Feb 26, 2021 20:12:37Latest reply: Oct 19, 2021 12:55:44 471 8 0 0 0
  Rewarded HiCoins: 0 (problem resolved)

please help me with this alarm , grid code EN 50549-1, inverter sun2000-6ktl-l1

Featured Answers

Recommended answer

BetterMing
Created Feb 27, 2021 00:46:06

Hello, dear.

You can refer to the following information.

2039 Output Overcurrent Alarm

Attribute

Alarm ID

Alarm Severity

2039

Major

Possible Causes

The power grid voltage drops dramatically or the power grid is short-circuited. As a result, the inverter transient output current exceeds the upper threshold and therefore the inverter protection is triggered.

Procedure

  1. The inverter detects its external working conditions in real time. After the fault is rectified, the inverter automatically recovers.

  2. If the alarm occurs frequently and affects the power production of the PV plant, check whether the output is short-circuited. If the fault persists, contact Huawei technical support.

This alarm may be caused by unstable power grids. You need to respond to the local grid.

View more
  • x
  • convention:

All Answers

grid voltage

grid voltage is above 250 volts,

View more
  • x
  • convention:

Tang_li
Tang_li Created Feb 27, 2021 03:22:21 (0) (0)
The voltage exceeds the protection voltage of the inverter.  

Hello, dear.

You can refer to the following information.

2039 Output Overcurrent Alarm

Attribute

Alarm ID

Alarm Severity

2039

Major

Possible Causes

The power grid voltage drops dramatically or the power grid is short-circuited. As a result, the inverter transient output current exceeds the upper threshold and therefore the inverter protection is triggered.

Procedure

  1. The inverter detects its external working conditions in real time. After the fault is rectified, the inverter automatically recovers.

  2. If the alarm occurs frequently and affects the power production of the PV plant, check whether the output is short-circuited. If the fault persists, contact Huawei technical support.

This alarm may be caused by unstable power grids. You need to respond to the local grid.

View more
  • x
  • convention:

what is Your problem ?
View more
  • x
  • convention:

2039

alarm occur when production is over 5 kw

View more
  • x
  • convention:

Confucius
Confucius Moderator Created Mar 3, 2021 09:16:14

@user_4133163


Please connect locally to your inverter (as an Installer) and then change it from General-EN50549-LV to General-IEC61727.

Then you can monitor it for few days to see how it behaves. Anyway, since 26/02/2021 13:13:19, it stopped to report any Output Overcurrent alarm.

Also, started with 28 Feb 2021, inverter had some DC Arc Fault alarms on string No.2, if still persist please ask the installer to check the installation on the DC side (both strings) to be sure that there is no problem (faulty DC cable, connector, water ingress etc).

Waiting your feedback!

View more
  • x
  • convention:

Hello, did you fix the problem with Output Overcurrent alarm id 2039? I have the same issue. Please advice
View more
  • x
  • convention:

Tang_li
Tang_li Created Oct 20, 2021 02:10:40 (0) (0)
You can send an email to the following email address, describing your problem and including your SN number.

Europe Email: eu_inverter_support@huawei.com

China and Asia Pacific: solarservice@huawei.com

Latin America: Email: la_inverter_support@huawei.com  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.