[Operation and Maintenance] Common UPS maintenance practices

Latest reply: Apr 11, 2022 06:21:10 144 1 1 0 0

Friends of the forum. Hi guys, today I will share the common UPS maintenance operations.


1、UPS switch maintenance bypass operation method

(1) Switching to the maintenance bypass power supply operation.

① switch the UPS to Static bypass

②Close the maintenance switch SWMB

③Unplug the module to be repaired and place it for 5 minutes to be discharged for repair


(2) Restore the utility inverter after the repair is completed.

① Switch the UPS to Static bypass

② Disconnect the maintenance switch SWMB, need to ensure that the UPS has no abnormal alarms.

③ switch the UPS to the main inverter power supply


2. How to hot-swap the power modules of modular UPS

(1) Procedure for unplugging power modules

① Turn the module ready switch to the OFF position first


1


②Pull out the module, and slow down the speed of pulling out when the module is half pulled out

③When the module lock appears near the exit, press down the module lock by hand and pull out the module at the same time


2


(2) Steps for inserting modules


3


①Turn the module ready switch to OFF position first

②Push the module into the slot slowly and evenly until it reaches the bottom and can no longer be pushed in.

③Turn the module ready switch to the ON position

④Lock the screws at the module lugs

Note: Before pushing the module into the cabinet, you need to check the module ready switch and push it into the cabinet only when it is in the OFF position.


3. Module replacement method-MDU



33


The display module maintenance steps are as follows:

1 Operate the LCD display to manually turn off the inverter so that the UPS turns to bypass power.

2: Close the maintenance bypass switch to turn the UPS to maintenance bypass power.

3 Export the monitoring configuration and store it on a USB flash drive.

4 Pull out the communication cable of the display module, loosen the fixing screw to replace the display module and reconnect the communication cable.

5: Import the configuration via USB flash drive

6 Disconnect the maintenance bypass and bypass power to the system. Manually turn on the inverter, UPS to inverter power supply. The system resumes power supply.

Caution:

Whether the program version of the MDU before and after replacement is consistent, if the version is not consistent, you need to pay attention to the compatibility with the existing system running program


That's all I have to share today, thanks for reading!


The post is synchronized to: uninterruptible power supply 2000/5000

Thanks for sharing.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.