Hi, Community!

This is a case about OceanStor Dorado V6 series DSM fails to start.

Symptoms

The customer manually removes and inserts the two controllers, causing the startup failure. Log in to the controller and enter the minisystem mode. The status of the switch failure is DSM startwork.

Cause

After the controller is reset unexpectedly, the DSM module in the system fails to be restored.

Analysis

1. Run the showsysstatus command in minisystem mode to check whether the controller you have logged in to is the master controller. That is, the role of the current node is master.


1


                                             

2. Run the sys.sh showflowtrace command in minisystem mode on the MPU to check whether the flow ID is 2.


2


3. Log in to the minisystem mode of all controllers and run the sys.sh showflowtrace 2 command to check whether the power-on failure phase is FAIL ACTION: DSMStartWork.

3

Run the plog.sh showstatus command in minisystem mode to check whether dirty data exists on the UMM and the dirty data status fails to be restored.

4

Solution

Clear the dirty data flag and power on the switch again.

1. Run the stream.sh deletedb all command on any controller.

5

2.  After the command is successfully executed, run the plog.sh forcepoweron command.

6

3. Run the rebootsys command to restart the controllers in minisystem mode. Wait until the controller is powered on again.

Post-Recovery Check

Run the showsysstatus command to check whether all controllers are in the Normal state.

7


We warmly welcome you to enjoy our community!



Comment

You need to log in to comment to the post Login | Register

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.