Neteco shows 0 isolation resistance for inverters

376 0 0 0 0

Isolation - specifies the inverter working mode based on the grounding status at the DC side and the connection to the power grid.


As we can see below, the inverter is running properly even if the isolation value is 0. How is it possible?


041959ha2q6dn66dkbkkus.png?Capture2.PNG


In this situation, we need to check the isolation parameter. Let's have a look:


042911h3qejjxxfxqme6xx.png?Capture3.PNG


As we know, before the start-up, inverters are performing auto-check tests to be sure that all the parameters meet the requirements that are checked before running. Among this, the inverter performs an isolation test.

If the isolation parameter is set as Input Grounded (with TF), the inverter will not perform the iso test anymore. This is the reason of the 0 isolation value shown in Neteco.


Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.