Installation Requirements
Table 1-2 Installation requirements
Installation Mode | Rack-mounted |
Height Difference Between Indoor and Outdoor Units | l If the outdoor unit is placed higher than the indoor unit, the vertical distance between them should be less than or equal to 20 m. l If the indoor unit is placed higher than the outdoor unit, the vertical distance between them should be less than or equal to 5 m. |
Maximum Equivalent Length of One-way Pipe | 60 m |
Thermal Insulation Foam Thickness | ≥ 13 mm |
Water Supply | The inlet water pressure should be 0.1–0.7 MPa, and the temperature should be in the range of 1°C–40°C. The wet film humidifier should use tap water that meets the following requirements: l Non-freezing and nephelometric turbidity units (NTU) < 3 l No visible substances. l 6.5 ≤ pH value ≤ 8.5 l Total hardness (in CaCO3) ≤ 450 mg/L |
Ports
Table 1-3 Ports
Item | Specifications |
Refrigerant gas pipe | Reserved port: 5/8 inch; thread connection (Table 2-6 lists the materials to be prepared onsite.) |
Refrigerant liquid pipe | Reserved port: 3/8 inch; thread connection (Table 2-6 lists the materials to be prepared onsite.) |
Humidifier water inlet pipe | Reserved port: G 1/2 inch, thread connection |
Condensate pump drainpipe | Reserved port: BSPT 1/2 inch, thread connection |
Pipe and cable routing | Top or bottom routing is supported. |
Table 1-4 Technical specifications
Item | NetCol5000-A010H61301W120E1 | NetCol5000-A010H613010020E1 |
Power system | 220–240 V AC, 50 Hz, 1P+N+PE | 220–240 V AC, 50 Hz, 1P+N+PE |
Voltage tolerance | The voltage threshold ranges from 187 V to 264 V. If front-end voltage fluctuation exceeds this range, you are advised to add a voltage regulator. Otherwise, the air conditioner may generate alarms frequently and fail to work properly. |
Frequency tolerance | ±3 Hz |
Certification | REACH, RoHS, CE, CCC |
Maximum current | 18.5 A | 4.5 A |
Cooling mode | Air cooling | Air cooling |
Refrigerant | R410A | R410A |
Cooling capacity | 11 kWa | 11 kWa |
Humidification | Supported | Not supported |
Humidifier capacity | 1.0 kg/h | - |
Heating | Supported | Not supported |
Heating capacity | 3 kW | - |
Air supply mode | Horizontal air supply | Horizontal air supply |
Fan type | DC fan | DC fan |
Maximum airflow | 2600 m3/h | 2600 m3/h |
Condensate pump | Supported | Supported |
Power supply mode | Single-route power supply | Single-route power supply |
Outline dimensions (H x W x D) | 442 mm x 442 mm x 800 mm | 442 mm x 442 mm x 800 mm |
Package dimensions (H x W x D) | 710 mm x 610 mm x 1000 mm | 710 mm x 610 mm x 1000 mm |
Net weight/Gross weight | 60 kg/79 kg | 57 kg/75 kg |
a: The cooling capacity is obtained from the 10 m pipes when the indoor dry bulb temperature is 37.8°C, indoor wet bulb temperature is 20.8°C, and outdoor dry bulb temperature is 35°C. The actual cooling capacity varies depending on the indoor and outdoor ambient temperatures and relative humidity. |
Table 1-5 Derating coefficient
Height | 0 | 1000 | 1500 | 2000 | 2500 | 3000 | 3500 | 4000 |
Density coefficient | 1 | 0.887 | 0.835 | 0.785 | 0.737 | 0.692 | 0.649 | 0.608 |
Air volume coefficient | 1 | 0.887 | 0.835 | 0.785 | 0.737 | 0.692 | 0.649 | 0.608 |
Cooling capacity coefficient | 1 | 0.940 | 0.909 | 0.878 | 0.846 | 0.815 | 0.784 | 0.753 |
Table 1-6 lists the specifications of the outdoor unit.
Table 1-6 Technical specifications
Item | Specifications |
Maximum operating current | 24 A |
Number of fans | One |
Outline dimensions (H x W x D) | 966 mm x 1057 mm x 339 mm |
Package dimensions (H x W x D) | 1210 mm x 1105 mm x 435 mm |
Net weight/Gross weight | 83 kg/99 kg |
Certification | REACH, RoHS, CE, CCC |
Operating temperature | –20°C to +45°C |
Storage temperature | –40°C to +55°C (with refrigerant)/70°C (without refrigerant) |
Storage humidity | 5–95% RH (non-condensing) |
Protection level | IPX4 |
Altitude | 0 m to 4000 m (The power should be derated when the altitude exceeds 1000 m. For details on derating, contact Huawei technical support.)
|