NetCol5000 air conditioning duct problem

Created: Mar 13, 2020 06:45:17Latest reply: Mar 13, 2020 07:05:34 410 2 0 0 0
  Rewarded HiCoins: 5 (problem resolved)

Hi, guys!

Can anyone tell me what is the maximum allowable length of NetCol5000 air conditioning ducts?

Thanks in advance!

Featured Answers

Installation Requirements

Table 1-2 Installation requirements

Installation Mode

Rack-mounted

Height Difference Between Indoor and Outdoor Units

l  If the outdoor unit is placed higher than the indoor unit, the vertical distance between them should be less than or equal to 20 m.

l  If the indoor unit is placed higher than the outdoor unit, the vertical distance between them should be less than or equal to 5 m.

Maximum Equivalent Length of One-way Pipe

60 m

Thermal Insulation Foam Thickness

≥ 13 mm

Water Supply

The inlet water pressure should be 0.1–0.7 MPa, and the temperature should be in the range of 1°C–40°C.

The wet film humidifier should use tap water that meets the following requirements:

l  Non-freezing and nephelometric turbidity units (NTU) < 3

l  No visible substances.

l  6.5 ≤ pH value ≤ 8.5

l  Total hardness (in CaCO3) ≤ 450 mg/L

Ports

Table 1-3 Ports

Item

Specifications

Refrigerant gas pipe

Reserved port: 5/8 inch; thread connection (Table 2-6 lists the materials to be prepared onsite.)

Refrigerant liquid pipe

Reserved port: 3/8 inch; thread connection (Table 2-6 lists the materials to be prepared onsite.)

Humidifier water inlet pipe

Reserved port: G 1/2 inch, thread connection

Condensate pump drainpipe

Reserved port: BSPT 1/2 inch, thread connection

Pipe and cable routing

Top or bottom routing is supported.

 

Table 1-4 Technical specifications

Item

NetCol5000-A010H61301W120E1

NetCol5000-A010H613010020E1

Power system

220–240 V AC, 50 Hz, 1P+N+PE

220–240 V AC, 50 Hz, 1P+N+PE

Voltage tolerance

The voltage threshold ranges from 187 V to 264 V. If front-end voltage fluctuation exceeds this range, you are advised to add a voltage regulator. Otherwise, the air conditioner may generate alarms frequently and fail to work properly.

Frequency tolerance

±3 Hz

Certification

REACH, RoHS, CE, CCC

Maximum current

18.5 A

4.5 A

Cooling mode

Air cooling

Air cooling

Refrigerant

R410A

R410A

Cooling capacity

11 kWa

11 kWa

Humidification

Supported

Not supported

Humidifier capacity

1.0 kg/h

-

Heating

Supported

Not supported

Heating capacity

3 kW

-

Air supply mode

Horizontal air supply

Horizontal air supply

Fan type

DC fan

DC fan

Maximum airflow

2600 m3/h

2600 m3/h

Condensate pump

Supported

Supported

Power supply mode

Single-route power supply

Single-route power supply

Outline dimensions (H x W x D)

442 mm x 442 mm x 800 mm

442 mm x 442 mm x 800 mm

Package dimensions (H x W x D)

710 mm x 610 mm x 1000 mm

710 mm x 610 mm x 1000 mm

Net weight/Gross weight

60 kg/79 kg

57 kg/75 kg

a: The cooling capacity is obtained from the 10 m pipes when the indoor dry bulb temperature is 37.8°C, indoor wet bulb temperature is 20.8°C, and outdoor dry bulb temperature is 35°C. The actual cooling capacity varies depending on the indoor and outdoor ambient temperatures and relative humidity.

 

Table 1-5 Derating coefficient

Height

0

1000

1500

2000

2500

3000

3500

4000

Density coefficient

1

0.887

0.835

0.785

0.737

0.692

0.649

0.608

Air volume coefficient

1

0.887

0.835

0.785

0.737

0.692

0.649

0.608

Cooling capacity coefficient

1

0.940

0.909

0.878

0.846

0.815

0.784

0.753

 

1.6 Outdoor Unit Specifications

Table 1-6 lists the specifications of the outdoor unit.

Table 1-6 Technical specifications

Item

Specifications

Maximum operating current

24 A

Number of fans

One

Outline dimensions (H x W x D)

966 mm x 1057 mm x 339 mm

Package dimensions (H x W x D)

1210 mm x 1105 mm x 435 mm

Net weight/Gross weight

83 kg/99 kg

Certification

REACH, RoHS, CE, CCC

Operating temperature

–20°C to +45°C

Storage temperature

–40°C to +55°C (with refrigerant)/70°C (without refrigerant)

Storage humidity

5–95% RH (non-condensing)

Protection level

IPX4

Altitude

0 m to 4000 m (The power should be derated when the altitude exceeds 1000 m. For details on derating, contact Huawei technical support.)



View more
  • x
  • convention:

All Answers

Hi
please find below link for NEtColl 5000 complete configuration and istallation guide.

https://support.huawei.com/enterprise/en/doc/EDOC1000143982

View more
  • x
  • convention:

Installation Requirements

Table 1-2 Installation requirements

Installation Mode

Rack-mounted

Height Difference Between Indoor and Outdoor Units

l  If the outdoor unit is placed higher than the indoor unit, the vertical distance between them should be less than or equal to 20 m.

l  If the indoor unit is placed higher than the outdoor unit, the vertical distance between them should be less than or equal to 5 m.

Maximum Equivalent Length of One-way Pipe

60 m

Thermal Insulation Foam Thickness

≥ 13 mm

Water Supply

The inlet water pressure should be 0.1–0.7 MPa, and the temperature should be in the range of 1°C–40°C.

The wet film humidifier should use tap water that meets the following requirements:

l  Non-freezing and nephelometric turbidity units (NTU) < 3

l  No visible substances.

l  6.5 ≤ pH value ≤ 8.5

l  Total hardness (in CaCO3) ≤ 450 mg/L

Ports

Table 1-3 Ports

Item

Specifications

Refrigerant gas pipe

Reserved port: 5/8 inch; thread connection (Table 2-6 lists the materials to be prepared onsite.)

Refrigerant liquid pipe

Reserved port: 3/8 inch; thread connection (Table 2-6 lists the materials to be prepared onsite.)

Humidifier water inlet pipe

Reserved port: G 1/2 inch, thread connection

Condensate pump drainpipe

Reserved port: BSPT 1/2 inch, thread connection

Pipe and cable routing

Top or bottom routing is supported.

 

Table 1-4 Technical specifications

Item

NetCol5000-A010H61301W120E1

NetCol5000-A010H613010020E1

Power system

220–240 V AC, 50 Hz, 1P+N+PE

220–240 V AC, 50 Hz, 1P+N+PE

Voltage tolerance

The voltage threshold ranges from 187 V to 264 V. If front-end voltage fluctuation exceeds this range, you are advised to add a voltage regulator. Otherwise, the air conditioner may generate alarms frequently and fail to work properly.

Frequency tolerance

±3 Hz

Certification

REACH, RoHS, CE, CCC

Maximum current

18.5 A

4.5 A

Cooling mode

Air cooling

Air cooling

Refrigerant

R410A

R410A

Cooling capacity

11 kWa

11 kWa

Humidification

Supported

Not supported

Humidifier capacity

1.0 kg/h

-

Heating

Supported

Not supported

Heating capacity

3 kW

-

Air supply mode

Horizontal air supply

Horizontal air supply

Fan type

DC fan

DC fan

Maximum airflow

2600 m3/h

2600 m3/h

Condensate pump

Supported

Supported

Power supply mode

Single-route power supply

Single-route power supply

Outline dimensions (H x W x D)

442 mm x 442 mm x 800 mm

442 mm x 442 mm x 800 mm

Package dimensions (H x W x D)

710 mm x 610 mm x 1000 mm

710 mm x 610 mm x 1000 mm

Net weight/Gross weight

60 kg/79 kg

57 kg/75 kg

a: The cooling capacity is obtained from the 10 m pipes when the indoor dry bulb temperature is 37.8°C, indoor wet bulb temperature is 20.8°C, and outdoor dry bulb temperature is 35°C. The actual cooling capacity varies depending on the indoor and outdoor ambient temperatures and relative humidity.

 

Table 1-5 Derating coefficient

Height

0

1000

1500

2000

2500

3000

3500

4000

Density coefficient

1

0.887

0.835

0.785

0.737

0.692

0.649

0.608

Air volume coefficient

1

0.887

0.835

0.785

0.737

0.692

0.649

0.608

Cooling capacity coefficient

1

0.940

0.909

0.878

0.846

0.815

0.784

0.753

 

1.6 Outdoor Unit Specifications

Table 1-6 lists the specifications of the outdoor unit.

Table 1-6 Technical specifications

Item

Specifications

Maximum operating current

24 A

Number of fans

One

Outline dimensions (H x W x D)

966 mm x 1057 mm x 339 mm

Package dimensions (H x W x D)

1210 mm x 1105 mm x 435 mm

Net weight/Gross weight

83 kg/99 kg

Certification

REACH, RoHS, CE, CCC

Operating temperature

–20°C to +45°C

Storage temperature

–40°C to +55°C (with refrigerant)/70°C (without refrigerant)

Storage humidity

5–95% RH (non-condensing)

Protection level

IPX4

Altitude

0 m to 4000 m (The power should be derated when the altitude exceeds 1000 m. For details on derating, contact Huawei technical support.)



View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.