Hello, one of the reasons for this warning may be that the communication between the off-management alarm network element and the network management is interrupted.

Step 1: Check the ML-PPP port status of NE10 and find that there is no problem with the link and the business is normal all the time. Eliminate DCN channel quality problems.
Step 2: Check the network element IP of NE30 and find that the core route of a DCN channel is repeated with that of NE10. It is confirmed that the setting of NE30 network element IP is wrong.
Step 3: Change the network element IP of NE30 on the network management. After the prompt is returned successfully, it is found that the two network elements are still intermittently de-managed.
Step 4: Try to query the information of NE30 network element. The IP of NE30 network element is still the error value before modification. The operation of network administrator to modify the IP of NE30 network element is not successful.
Step 5: Repeat the operation of modifying NE30 network element IP several times until the intermittent network element de-piping failure disappears.
I hope I can help you.