ISSUE DESCRIPTION


After the equipment room failed to be powered, 62 hosts on the live network failed to recover after the power supply was restored.


host fault


FAULT LOCATION


1. Logged in to the first node from the background and pinged the internal_base and external_OM of the faulty host:


internal_base


Checked the switch status on eSight. 9 switches were not restored.


switch status


2. After the switch configuration had been restored, the host fault was rectified and 18 VMs were in the error and rebuild the state:


switch configuration is restored


Volume device not found:


Volume device not found


Volume mounting exception

3. The storage service IP address was unavailable because storage controller B was faulty.


storage controller B


storage controller B


storage controller B


4. The last VM was not recovered. No path could be found after the upadmin show vlun command was run on the host. The interconnected storage was FC SAN. The port on the host side was online, while the port on the SNS side was offline.


4) The last VM is not recovered. No path can be fo


The zone configuration on the SNS was not added. After the zone configuration had been added, the VM was restored.


SOLUTION


1. Restore the switch configuration using the historical backup file on the switch side.


2. After the data plane IP address of the faulty controller is removed from the FusionSphere interconnection configuration, 14 VMs are automatically restored.


3. After the zone configuration is added to the SNS switch, 1 CEP VM is automatically restored.


TO CHECK AFTER RECOVERY


Remind the service side to check the service recovery status first.


This is my solution, how about yours? Go ahead and share it with us!

The post is synchronized to: Huawei Cloud Computing Case

  • x
  • convention:

user_4000619
Moderator Created May 26, 2022 23:27:14

thanks
View more
  • x
  • convention:

olive.zhao
olive.zhao Created May 27, 2022 08:40:12 (0) (0)
 
Saqibaz
Created May 27, 2022 06:48:57

Great share
View more
  • x
  • convention:

olive.zhao
olive.zhao Created May 27, 2022 08:40:23 (0) (0)
Thanks!  
Suhail
Created Jun 1, 2022 07:04:40

Thank you for providing such valuable information.
View more
  • x
  • convention:

olive.zhao
olive.zhao Created Jun 6, 2022 08:27:36 (0) (0)
 
little_fish
Admin Created Jun 2, 2022 04:07:49

Thanks.
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.
Information Protection Guide
Thanks for using Huawei Enterprise Support Community! We will help you learn how we collect, use, store and share your personal information and the rights you have in accordance with Privacy Policy and User Agreement.