Hello, everyone!

 

This post will tell you one issue for MSP ring offline due to AUX fault.

Problem description:

Customer report that 4 nodes offline in MSP ring (303, 308, 309, 310)

Version: 5.21.18.55

All node of Ring exist with 1+0 GSCC. 

 Handling procedure:

1) Check the Aggregation node 303 of the ring.

2) Check the GSCC of the 303 NE, Found PROG LED of GSCC RED.

3) We replace the GSCC and download the data on new GSCC after version match.

4) Boards are still not appear on NMS except GSCC FAN and AUX, remaining boards have communication alarm.

5) Replace the AUX board and the board are normal.

6) Revert the old GSCC that also working fine and all NEs are online.

Root cause:

AUX faulty.

Solution:

AUX board replaced.  

That's all, I welcome everyone to leave a message and exchange in the comment area!

 

Thank you

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.