Almos all alarms generated by Huawei Inverters or Smart Loggers, are automatically cleared when the fault disappear.
There are also some alarms that must be manually clear after the fault is rectified.
An example for this type of alarm is “DC Arc fault alarm”.
After the DC strings connection and insulation resistance tests are performed, the alarm should be manually cleared from Inverter or Smart Logger settings .
Procedure for clear the alarms for Smart Logger 3000
1. Login on Smartlogger3000
Plug in an Ethernet cable between personal computer and Smart Logger LAN port.
Before connect on WebUi of Smartlogger3000, set your local area connection of your computer with an IP in the same range like Smart Logger 3000 (default LAN IP 192.168.8.10):
Control Panel-> Network and Internet-> Network and Sharing Center-> Change adapter settings-> Local Area Connection (Ethernet) ->Properties on Internet Protocol Version 4 and set the IP 192.168.8.15 :

2. Connect Ethernet cable in LAN PORT and open the next link in a browser (Chrome or IE) https://192.168.8.10 and login as admin with the default password “Changeme”

3. Maintenance -> Device Mgmt.-> Clear Alarm