I need you to provide more information about the alert. Such as alarm name or alarm code.
Maybe you can refer to the following information:
Solution
Possible Causes:
1) The AC Undervoltage alarm threshold is not set properly on the SMU.
2) The power grid is faulty.
Measures:
1) Check whether the AC Undervoltage alarm threshold is properly set. If no, adjust it to a proper value.
2) Check whether the AC input voltage is below the AC Undervoltage alarm threshold (180V AC by default). If yes, handle the AC input fault.