LUNA2000 shutting down when discharged

Created: Oct 20, 2021 06:09:47Latest reply: Oct 21, 2021 11:56:26 584 11 0 0 0
  Rewarded HiCoins: 0 (problem resolved)

Hi,


We have the following problem. We have installed a LUNA2000 5kW in a solar system with 5KTL-L1.

We are experiencing the following problem - when the battery discharges to a low level it shuts down on its own and it won't go back on until you physically turn it on with the button on the side.

Does anybody know why is that? How can it be prevented, as we are going there for 4th time just to turn on the battery which is quite annoying..

Thanks!


Featured Answers
Confucius
Moderator Created Oct 21, 2021 11:56:26

@Alexand3r your inverter has an active alarm - 2068 / ID 3 - Battery Abnormal, which means that the inverter and the DCDC EN line is abnormal.

You should ask your installer to come back and check the communication between inverter and battery's DCDC unit, on the L1 inverters is like the below diagram:

1

Also, the inverter should be upgraded to the latest firmware version (SPC112), your installer can do it remotely via FusionSolar management system.

View more
  • x
  • convention:

Alexand3r
Alexand3r Created Oct 22, 2021 05:49:29 (1) (0)
Hi. Thanks, I think that is the problem. We are the installer, but I think there might be a missed communication cable between 6)EN and 3) on the battery. Will fix that and will see. Thanks again.  
Confucius
Confucius Reply Alexand3r  Created Oct 22, 2021 08:45:32 (0) (0)
You're welcome!  

Recommended answer

Tang_li
Admin Created Oct 20, 2021 06:42:08

You can remotely check the backup SOC and cut-off SOC on FusionSolar 7.0.
Check whether alarm 2068-3 is generated on the inverter and whether the EN enable cable between the inverter and LUNA is disconnected.

View more
  • x
  • convention:

Tang_li
Tang_li Created Oct 20, 2021 06:48:30 (0) (0)
Waiting for your feedback  
All Answers
Hi, dear

Please kindly wait for a minute.
View more
  • x
  • convention:

 the backup SOC. In grid-tied mode, the energy storage is not discharged when it reaches the backup SOC. When the grid is powered off, the energy storage system supplies power to loads in backup mode. The priority of Backup SOC is higher than that of Discharge Cut-off SOC. For example, if Discharge Cut-off SOC is set to 10% and Backup SOC is set to 20%, the battery will not be discharged when the battery discharge reaches 20%.

View more
  • x
  • convention:

You can remotely check the backup SOC and cut-off SOC on FusionSolar 7.0.
Check whether alarm 2068-3 is generated on the inverter and whether the EN enable cable between the inverter and LUNA is disconnected.

View more
  • x
  • convention:

Tang_li
Tang_li Created Oct 20, 2021 06:48:30 (0) (0)
Waiting for your feedback  

FS


Can you tell me where in FusionSolar I can check that remotely, because I don't see it? Thanks!

View more
  • x
  • convention:

Tang_li
Tang_li Created Oct 21, 2021 02:56:24 (0) (0)
Maintenance-Alarm Management:You can see the alarm information of the device.
Plant -device management-(After you select a device-LUNA)-set parameters  
Hi, there is no such menu as "Set Parameters" when I open the battery trough the Device Management menu. You can see it on the screenshot I attached. I can only look at battery data, but cannot operate anything.
View more
  • x
  • convention:

Confucius
Confucius Created Oct 21, 2021 11:45:49 (0) (0)
@Alexand3r that's because you have an Owner account.  
Confucius
Confucius Moderator Created Oct 21, 2021 11:56:26

@Alexand3r your inverter has an active alarm - 2068 / ID 3 - Battery Abnormal, which means that the inverter and the DCDC EN line is abnormal.

You should ask your installer to come back and check the communication between inverter and battery's DCDC unit, on the L1 inverters is like the below diagram:

1

Also, the inverter should be upgraded to the latest firmware version (SPC112), your installer can do it remotely via FusionSolar management system.

View more
  • x
  • convention:

Alexand3r
Alexand3r Created Oct 22, 2021 05:49:29 (1) (0)
Hi. Thanks, I think that is the problem. We are the installer, but I think there might be a missed communication cable between 6)EN and 3) on the battery. Will fix that and will see. Thanks again.  
Confucius
Confucius Reply Alexand3r  Created Oct 22, 2021 08:45:32 (0) (0)
You're welcome!  

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.