1. Problem Description

A customer reported that the reactive power output of the SUN2000-60KTL-M0 was abnormal and did not respond to the background reactive power scheduling.

 

2. Problem Analysis

First.          The customer uses the SmartLogger to issue reactive power output commands. Among the nine inverters onsite, the output of six inverters is normal, and the output of three inverters does not respond to reactive power commands.

5

1

Second.      According to the log and packet information of the SmartLogger, the reactive power command has been delivered to the inverter. Therefore, the SmartLogger is not faulty.

 2

Third.      According to the inverter logs, the inverter has received the command but has not executed it.

The inverter receives the instruction with PF=0.94 from 2021/3/27 15:09:48 to 2021/3/27 15:22:28. According to the current operating power, the inverter should normally generate more than 10kVA reactive power.

3

However, the inverter run log shows that the inverter does not generate reactive power.

6

The DSP log shows that the intelligent QU restricts the reactive power output of the inverter.

4

Fourth.   Check the run logs again. The onsite power grid voltage approaches or exceeds the level-1 overvoltage protection threshold of the inverter. It is suspected that the onsite power grid voltage is too high. To avoid further increase of the power grid voltage, the inverter limits the reactive power output.

8

1


Fifth.        To verify the speculation, the overvoltage protection threshold is temporarily adjusted to 260 V. Perform the test again. The inverter can execute the reactive power command normally.

2

3

Sixth.       The grid-tied voltages of the nine inverters on site differ slightly due to grid-tied points. By comparing the grid-tied voltages of the nine inverters on site, the grid-tied voltage of the inverters is lower than the grid-tied voltage of the abnormal inverters when the reactive power command is executed. As a result, some inverters do not execute reactive commands.

 

3. Fault Locating

Based on log analysis and on-site tests, it is determined that the on-site power grid voltage is close to the overvoltage protection threshold. Therefore, the inverter does not increase the on-site voltage and restrict the inverter's reactive power output.

 

4. Solution

1. Check whether the voltage at the grid-tied point is too high. If yes, contact the local power operator.

2. If the voltage at the grid-tied point is higher than the allowed range and the local power operator agrees, modify the overvoltage protection threshold.


Thanks for sharing
View more
  • x
  • convention:

thanks
View more
  • x
  • convention:

good
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.