Inverter Power Limit Failure Due to Background Time Synchronization Fault

230 0 0 0 0


Background:

In a project in Liaoning, a 28KTL inverter with no command and power limit was displayed. The inverter was connected to the background and Huawei SmartLogger.

Problem Analysis

According to the inverter logs, there are two data about the energy yield of the inverter every day.

112718liwx1xb83688ckxw.png,

 

The time synchronization between the NMS and the SmartLogger is incorrect. The SmartLogger time is changed, causing abnormal energy yield.

 

https://forum.huawei.com/enterprise/zh/data/attachment/forum/202003/31/111602pd78b3wg1wd7vh97.png

 

Cause: The time synchronization between the NMS and the SmartLogger is faulty. As a result, the energy yield data is abnormal, and the calculation result is abnormal.

 

Solution: Adjust the time on the back-end NMS to be the same as that on the SmartLogger.

 

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.