10  Device Management

10.1  AC Management

10.1.1  AC Configuration

Context

An AC manages APs, controls WLAN user access, and guarantees security. APs can communicate with the AC only after the basic AC attributes are configured.

Procedure

  1. Choose Device Management > AC Management > AC Configuration.

    Figure 10-1  AC Configuration 
    fbe513cf748349ee81f10226d0bac618

  2. On the AC Configuration tab page, set parameters described in Table 10-1.

    e991da38b658448691f93f865d88ccfd

  3. Click Apply.

    293ebd643f44442783a0e89f960612bb NOTICE:
    When the country code is changed on an AC, information about APs connected to the AC is deleted and the APs are reset.

    Table 10-1  AC configuration parameter

    Parameter

    Description

    ID

    AC ID.

    Country code

    AC country code.

    AP authentication mode

    Authentication mode used to authenticate APs. By default, the AC authenticates APs using MAC address authentication.

    NOTE:
    • MAC: The AP authentication mode can be set to MAC address authentication.
    • SN: The AP authentication mode can be set to SN authentication.
    • No authentication: The AP authentication mode can be set to non-authentication.

    AC source interface

    Source interface of the AC.
    • VLANIF: A VLANIF interface is used as the source interface.
    • LoopBack: A loopback interface is used as the source interface.
    • Virtual IP address: The virtual IP address of the VRRP group is used as the source interface.
    NOTE:
    The selected source interface must have an IP address.

    To delete the AC's source interface, click e96701bb9fe44b21a13c88695a76e082.

    AP data buffer

    Whether to enable the AC to buffer AP data.

    Buffer duration (min)

    Period during which the AC buffers AP data.

    Forwarding mode

    Forwarding mode of the AC.

10.2  AP Management

10.2.1  AP Information

Context

You can view information about the AP only after an AP goes online or add an AP offline.
293ebd643f44442783a0e89f960612bb NOTICE:
  • If the status of an AP is fault, the AP cannot be restarted.
  • During the restart, you are disconnected from the AP.

Procedure

  • Available APs

    • Adding an AP

    1. Choose Device Management > AP Management > AP Info.

      Figure 10-2  AP Info 
      5ab26c8bc44241ababc1082d6b7507e7

    2. In the Available APs area, click Create. In the Create AP dialog box that is displayed, set parameters. See Table 10-2 for description of the parameters.

      3f18f64a464044c69cf94d6b3f528fb5

    3. Click OK. The AP is added to the Available APs.

      Table 10-2  Parameters for adding an AP

      Parameter

      Description

      ID

      ID of an AP to be added.

      Name

      Name of an AP to be added.

      Type

      Type of an AP to be added.

      NOTE:
      If you select Customize, configure the name and type ID of the customized AP. The name must begin with WA, AP, wa, or ap.

      Type name

      Name of the self-defined AP to be added.

      Type ID

      ID of the self-defined AP to be added.

      MAC address

      MAC address of an AP to be added.

      NOTE:
      When the authentication mode is non-authentication on the AC, you must set MAC address or SN. When the authentication mode is MAC address authentication on the AC, you must set MAC address.

      SN

      SN of an AP to be added.

      NOTE:
      When the authentication mode is non-authentication on the AC, you must set MAC address or SN. When the authentication mode is SN authentication on the AC, you must set SN.

      Access-mode

      Radio that the AP allows STAs to use.
      • 2.4 GHz: STAs access the AP through the 2.4 GHz radio.
      • 5 GHz: STAs access the AP through the 5 GHz radio preferentially.
      NOTE:

      When the AP and STAs support both 5 GHz and 2.4 GHz, the AP can allow the STAs to access only the 5 GHz radio.

      AC priority

      Priority of the AC.

      NOTE:
      A smaller value indicates a higher priority.

      Region

      Region to which the AP is added.

      Profile

      Profile used by the AP.

    • Modifying an AP

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, click 03308b93a6c8407da26ea5ad46a026c1 corresponding to an AP.
    3. In the Modify AP dialog box that is displayed, set parameters described in Table 10-3. Parameter AP ID cannot be modified.

      2d93971b2ecf42088c20fca72a360147

    4. Click OK.

      Table 10-3  Parameters for modifying an AP

      Parameter

      Description

      ID

      ID of an AP.

      Name

      Name of an AP to be modified.

      Access mode

      Radio that the AP allows STAs to use.
      • 2.4 GHz: STAs access the AP through the 2.4 GHz radio.
      • 5 GHz: STAs access the AP through the 5 GHz radio.
      NOTE:
      When the AP and STAs support both 5 GHz and 2.4 GHz, the AP can allow the STAs to access only the 5 GHz radio.

      AC priority

      Priority of the AC.

      NOTE:
      A smaller value indicates a higher priority.

      Profile

      Profile used by the AP.

      Forwarding mode

      Data forwarding mode of an AP.

      This parameter cannot be set when service set-based forwarding is used.

      Channel bandwidth

      Channel bandwidth of the specified radio on the AP.

      Channel

      Channel of the specified radio on the AP.
      NOTE:
      After an AP region is configured, this parameter can be set to a channel supported by the AP region.

      Power level

      Power level of a specified radio on the AP.

      MCS value

      MCS value of a specified radio on the AP.
      NOTE:
      This parameter is available only when radio type is 802.11n, 802.11a/n, 802.11g/n, or 802.11b/g/n.

      Multicast MCS value

      Multicast MCS value of a specified radio on the AP.
      NOTE:
      This parameter is available only when radio type is 802.11n, 802.11a/n, 802.11g/n, or 802.11b/g/n.

      Multicast Rate value

      Multicast rate of a specified radio on the AP.
      NOTE:

      By default, the rate of wireless multicast packets is 11 Mbit/s for a 80211b, 80211bg, 80211bgn, or 80211n radio and 6 Mbit/s for radios of other types.

      If you configure the maximum rate for a radio but the radio does not support the configured maximum rate, the configuration fails.

      MCS value and rate of multicast packets cannot be configured simultaneously.

      Multi-user traffic load balancing

      Whether to enable the multi-user load balancing function.

      AP wired interface working mode

      Working mode of an AP wired interface.
      • root: The wired interface connects to the AC.
      • endpoint: The wired interface connects to a host or Layer 2 network.

      AP wired interface user isolate

      User isolation on an AP wired interface.

      The user isolation function prevents STAs associated with the same AP from forwarding Layer 2 packets to each other. This function ensures communication security on wired interfaces and allows uniform charging for users.

      NOTE:
      Before you enable user isolation on an AP wired interface, the AP wired interface must work in endpoint mode.

      AP wired interface STP

      STP function on an AP wired interface.

      The STP function prevents loops on the network.

      Default VLAN

      Default VLAN on an AP wired interface.

      Untagged VLAN

      Wired interfaces are added to a VLAN in untagged mode.

      Tagged VLAN

      Wired interfaces are added to a VLAN in tagged mode.

    • Replacing an AP

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, click a6466053bbe34c8ebc38c3698280554d corresponding to an AP.
    3. In the AP Replace dialog box that is displayed, set parameters described in Table 10-4.

      Table 10-4  Parameters for replacing an AP

      Parameter

      Description

      MAC address

      MAC address of the new AP. If the MAC address is null, the MAC address of the AP remains unchanged. If MAC address authentication is used, the MAC address cannot be null.

      SN

      SN of the new AP. If the SN is null, the SN of the AP remains unchanged. If SN authentication is used, the SN cannot be null.

    • Deleting an AP

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, select an AP and click Delete. In the Information dialog box that is displayed, click OK.

    • Restarting an AP

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, select an AP to be restarted and click Restart. In the Information dialog box that is displayed, click OK.

    • Restarting all APs

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, click Restart All APs. In the Information dialog box that is displayed, click OK.

    • Adding an AP to a specified AP region

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, select an AP and click Add to Region. In the AP Region listdialog box that is displayed, select a region and click OK.

    • Delivering configurations to an AP

    1. Choose Device Management > AP Management > AP Info.
    2. In the Available APs area, select an AP and click Commit Configuration. In the Information dialog box that is displayed, click OK.

    • Searching for an AP

    1. Choose Device Management > AP Management > AP Info.
    2. Set Search and the query criteria, and click Go. You can view, modify, delete, restart, and deliver configurations to an AP, and add an AP to a region.
  • Unauthorized APs

    • Allowing an unauthorized AP to go online on an AC

    1. Choose Device Management > AP Management > AP Info.
    2. In the Unauthorized APs area, select an AP and click Confirm. In the Information dialog box that is displayed, click OK.

    • Allowing all unauthorized APs to go online on an AC

    1. Choose Device Management > AP Management > AP Info.
    2. In the Unauthorized APs area, click Confirm All. In the Information dialog box that is displayed, click OK.

    • Adding unauthorized APs to the MAC address whitelist and SN whitelist.

    1. Choose Device Management > AP Management > AP Info.
    2. In the Unauthorized APs area, click d43074a8d8304b6a91469afe36bcc479 located at the right of an AP. In the Add To Whitelist dialog box that is displayed, enter the MAC address and SN and click OK.

      b63e80a573a046d1b6c6dba67dcc2343

      8d4acb66be4847968bd3c3aafd332318 NOTE:
      If the AP authentication mode is set to non-authentication, either the MAC address or the SN must be entered; if the AP authentication mode is set to MAC authentication, the MAC address must be entered; if the AP authentication mode is set to SN authentication, the SN must be entered.

10.2.2  AP Region

Context

Adjusting the radio channel and power of an AP may lead to adjustment of another AP. To quicken adjustment, minimize the impact, and reduce the workload, all the APs accessing the same AC can be divided into several regions. The impact of adjustment on an AP is limited within the local region. An AP region can also be used for batch AP upgrade. You can upgrade APs of the same type in the same region in batches.

Procedure

  • Creating an AP region
    1. Choose Device Management > AP Management > AP Region.

      Figure 10-3  AP Region 
      017beeadd9f0464c97acb955d07b8793

    2. In the AP Region, click Create. In the Create AP Region dialog box that is displayed, set parameters described in Table 10-5.

      840cc1e73be2431aa3661ed37465e409

    3. Click OK. The AP region is added to the AP region list.

      Table 10-5  Parameters for creating an AP region

      Parameter

      Description

      Region ID

      ID of an AP region to be added.

      Region name

      Name of an AP region to be added.

      Deployment mode

      Deployment mode of an AP region. The default value is Common.

      Country code

      Country code specified for an AP region.

  • Modifying an AP region
    1. Choose Device Management > AP Management > AP Region.
    2. In AP Region, click 03308b93a6c8407da26ea5ad46a026c1 corresponding to an AP region.
    3. In the Modify AP Region dialog box that is displayed, set parameters described in Table 10-5. Parameter Region ID cannot be modified.

      d3b9eeae77674270abf822c1e191e819

    4. Click OK.
  • Deleting an AP region
    1. Choose Device Management > AP Management > AP Region.
    2. In the AP Region, select an AP region and click Delete. In the Information dialog box that is displayed, click OK.

      293ebd643f44442783a0e89f960612bb NOTICE:

      The configured default AP region, system default AP region, and AP regions contains any AP cannot be deleted.

  • Configuring the default AP region
    1. Choose Device Management > AP Management > AP Region.
    2. In AP Region, click 259109b42f5f4667b80b8b85b5a868be corresponding to an AP region to configure the region as the default region.
  • Configuring a calibration channel set in the AP region
    1. Choose Device Management > AP Management > AP Region.
    2. In AP Region, click 95d8a2e8ec4240a193f7d2d16774d415 corresponding to an AP region to configure a calibration channel set in the AP region.

      You can specify a calibration channel set for the AP. When implementing radio calibration, the device can select channels from the calibration channel set. This reduces the burden on the device. There are global calibration channel set and region calibration channel set.

      The device implements radio calibration according to the following principles:
      • If no country code is configured in the AP region, the device implements radio calibration on global calibration channels.
      • If a country code is configured in the AP region, the device implements radio calibration based on whether calibration channels are specified in the AP region.
        • If calibration channels are specified in the AP region, the device implements radio calibration only on channels specified in the AP region.
        • If no calibration channel is specified in the AP region, the device implements radio calibration on channels in the calibration channel set that corresponds to the country code in the AP region.
        • For configurations about the region calibration channel set, see Configuring a Calibration Channel Set in the AP Region in 10.2.2 AP Region.

      See 10.3.1 Radio Calibration for configurations of the global calibration channel set.

  • Searching for an AP region
    1. Choose Device Management > AP Management > AP Region.
    2. Set Search and the query criteria, and click Go. AP regions matching the query criteria are displayed. You can view, modify, and delete the AP regions.

10.2.3  AP Profile

Procedure

  • Creating an AP profile
    1. Choose Device Management > AP Management > AP Profile.

      Figure 10-4  AP Profile 
      dca6261d392f4b55b4f237d1e857f934

    2. In the AP Profile List area, click Create. In the Create AP Profile dialog box that is displayed, set parameters described in Table 10-6.

      de9e04c5ecbd49a99198f8c83ebdf88a

    3. Click OK. The AP profile is added to the AP profile list.

      Table 10-6  Parameters for creating an AP profile

      Parameter

      Description

      Profile name

      Name of an AP profile to be added.

      Eapol-response packet encapsulation

      Eapol-Response packet encapsulation mode.
      • If the authentication server can process only EAP broadcast packets, configure the AP to encapsulate Eapol-Response packets into broadcast packets.
      • If the authentication server can process only EAP multicast packets, configure the AP to encapsulate Eapol-Response packets into multicast packets.
      • If the authentication server can process only EAP unicast packets, configure the AP to encapsulate Eapol-Response packets into unicast packets with specified MAC addresses or MAC addresses learned by the AP.
      By default, an AP encapsulates Eapol-Response packets into unicast packets with MAC addresses learned by the AP.

      MAC address

      MAC address specified for Eapol-Response packets.

      Eapol-start packet encapsulation

      Eapol-Start packet encapsulation mode.
      • If the authentication server can process only EAP broadcast packets, configure the AP to encapsulate Eapol-Start packets into broadcast packets.
      • If the authentication server can process only EAP multicast packets, configure the AP to encapsulate Eapol-Start packets into multicast packets.
      • If the authentication server can process only EAP unicast packets, configure the AP to encapsulate Eapol-Start packets into unicast packets with specified MAC addresses.
      By default, an AP encapsulates Eapol-Start packets into multicast packets.

      MAC address

      MAC address specified for Eapol-Start packets.

      Eapol-response packet transform

      Eapol-Response packets to be transformed by the AP.
      • Specified: Configures the AP to transform only the Eapol-Response packets with the destination MAC address being the AP's BSSID.
      • All: Configures the AP to transform all Eapol-Response packets.
      By default, the AP transforms only the Eapol-Response packets with the destination MAC address being the AP's BSSID.

      Eapol-start packet transform

      Eapol-Start packets to be transformed by the AP.
      • Specified: Configures the AP to transform only the Eapol-Start packets with the destination MAC address being the AP's BSSID.
      • All: Configures the AP to transform all Eapol-Start packets.
      By default, the AP transforms only the Eapol-Start packets with the destination MAC address being the AP's BSSID.

      MTU(bytes)

      Specifies the maximum size of packets sent and received on an Ethernet port.

      Log backup mode

      Log backup mode. The value can be automatic backup or non-backup.

      By default, logs are auto backed up.

      Log backup server IP

      IP address of the log backup server.

      Offline management

      Whether to enable the offline management function.

      By default, offline management is disabled.

      Sampling interval (s)

      Sampling interval on an AP.

      Statistics interval (s)

      Interval for collecting statistics on an AP.

      4-way-handshake

      Specifies the device on which the key negotiation is performed when STAs using WPA/WPA2 authentication are roaming.

      By default, the key negotiation is performed on the AC when STAs using WPA/WPA2 authentication are roaming.

  • Modifying an AP profile
    1. Choose Device Management > AP Management > AP Profile.
    2. In AP Profile List area, click 03308b93a6c8407da26ea5ad46a026c1 corresponding to an AP profile.
    3. In the Modify AP Profile dialog box that is displayed, set parameters described in Table 10-6. Parameter Profile Name cannot be modified.

      f853015143084fd9b6981288bcb56b89

    4. Click OK.
  • Deleting an AP profile
    1. Choose Device Management > AP Management > AP Profile.
    2. In the AP Profile List area, select an AP profile and click Delete. In the Informationdialog box that is displayed, click OK.

      293ebd643f44442783a0e89f960612bb NOTICE:

      The configured default AP profile, system default AP profile, and bound AP profiles cannot be deleted.

  • Configuring the default AP profile
    1. Choose Device Management > AP Management > AP Profile.
    2. In AP Profile List area, click 259109b42f5f4667b80b8b85b5a868be corresponding to an AP profile to configure the profile as the default profile.
  • Searching for an AP profile
    1. Choose Device Management > AP Management > AP Profile.
    2. Set Profile name, and click Search. AP profiles matching the query criteria are displayed. You can view, modify, and delete the AP profiles.

10.2.4  AP Whitelist

Procedure

  • Adding an AP MAC address to the AP whitelist
    1. Choose Device Management > AP Management > AP Whitelist.

      Figure 10-5  AP Whitelist 
      9e45c59ae01447bbabda4ab3c0d751ff

    2. In the MAC Whitelist area, click Add. In the Add to MAC Whitelist dialog box that is displayed, set parameters described in Table 10-7.

      d2eed1024d1a48c7a82248b135c12fee

    3. Click OK. The AP MAC address is added to the AP whitelist.

      Table 10-7  Parameters for adding an AP MAC address to the AP whitelist

      Parameter

      Description

      MAC address

      MAC address of an AP to be added to the AP whitelist.

  • Adding AP MAC addresses to the AP whitelist in batches
    1. Choose Device Management > AP Management > AP Whitelist.
    2. In the MAC Whitelist area, click Batch Add. In the Batch Add to MAC Whitelist dialog box that is displayed, set parameters described in Table 10-8.

      296bca4d0be140be9a93a279fba50673

    3. Click OK. The AP MAC addresses are added to the AP whitelist.

      Table 10-8  Parameters for adding AP MAC addresses to the AP whitelist in batches

      Parameter

      Description

      Start MAC address

      Start MAC address when you add AP MAC addresses to the AP whitelist in batches.

      End MAC address

      End MAC address when you add AP MAC addresses to the AP whitelist in batches. The end MAC address must be larger than or equal to the start MAC address.
      • AC6605: A maximum of 512 MAC addresses can be added in batches.
      • AC6005: A maximum of 256 MAC addresses can be added in batches.

  • Deleting an AP MAC address from the AP whitelist
    1. Choose Device Management > AP Management > AP Whitelist.
    2. In the MAC Whitelist area, select an AP MAC address and click Delete. In the Information dialog box that is displayed, click OK.
  • Deleting AP MAC addresses from the AP whitelist in batches
    1. Choose Device Management > AP Management > AP Whitelist.
    2. In the MAC Whitelist area, click Batch Delete. In the Batch Delete MAC Whitelist dialog box that is displayed, set parameters described in Table 10-8.
    3. Click OK. The AP MAC addresses are deleted from the AP whitelist.
  • Searching for an AP MAC address in the AP whitelist
    1. Choose Device Management > AP Management > AP Whitelist.
    2. Set MAC address and click Search. You can delete the found AP MAC address from the AP whitelist.
  • Operations on the SN whitelist are similar to those on the AP whitelist.

    8d4acb66be4847968bd3c3aafd332318 NOTE:
    • When adding SNs to the whitelist in batches, ensure that the end SN is larger than or equal to the start SN and the two SNs are of the same length.
    • AC6605: A maximum of 512 SNs can be deleted in batches.
    • AC6005: A maximum of 256 SNs can be deleted in batches.

10.2.5  AP Blacklist

Procedure

  • Adding an AP MAC address to the AP blacklist
    1. Choose Device Management > AP Management > AP Blacklist.

      Figure 10-6  AP Blacklist 
      fa79f90a46bd419ea86bacd0b3906fa0

    2. In the MAC Blacklist area, click Add. In the Add to MAC Blacklist dialog box that is displayed, set parameters described in Table 10-9.

      f672076209e94547a25a0b2e605a8553

    3. Click OK. The AP MAC address is added to the AP blacklist.

      Table 10-9  Parameters for adding an AP MAC address to the AP blacklist

      Parameter

      Description

      MAC address

      MAC address of an AP to be added to the AP blacklist.

  • Adding AP MAC addresses to the AP blacklist in batches
    1. Choose Device Management > AP Management > AP Blacklist.
    2. In the MAC Blacklist area, click Batch Add. In the Batch Add to MAC Blacklist dialog box that is displayed, set parameters described in Table 10-10.

      93471579b65248a4aa6e2bae3af2ddc2

    3. Click OK. The AP MAC addresses are added to the AP blacklist.

      Table 10-10  Parameters for adding AP MAC addresses to the AP blacklist in batches

      Parameter

      Description

      Start MAC address

      Start MAC address when you add AP MAC addresses to the AP blacklist in batches.

      End MAC address

      End MAC address when you add AP MAC addresses to the AP blacklist in batches. The end MAC address must be larger than or equal to the start MAC address. A maximum of 128 MAC addresses can be added to the AP blacklist in batches.

  • Deleting an AP MAC address from the AP blacklist
    1. Choose Device Management > AP Management > AP Blacklist.
    2. In the MAC Blacklist area, select an AP MAC address and click Delete. In the Information dialog box that is displayed, click OK.
  • Deleting AP MAC addresses from the AP blacklist in batches
    1. Choose Device Management > AP Management > AP Blacklist.
    2. In the MAC Blacklist area, click Batch Delete. In the Batch Delete MAC Blacklist dialog box that is displayed, set parameters described in Table 10-10.
    3. Click OK. The AP MAC addresses are deleted from the AP blacklist.
  • Searching for an AP MAC address in the AP blacklist
    1. Choose Device Management > AP Management > AP Blacklist.
    2. Set MAC address and click Search. You can delete the found AP MAC address from the AP blacklist.

10.3  AP Maintenance

10.3.1  Radio Calibration

Procedure

  • Configure manual calibration.
    1. Click Device Management > AP Maintenance > Radio Calibration. The Radio Calibration page is displayed.

      5e9d7ee0c6494e7c8141ea0fd3590ce2

    2. In Radio Calibration Setting, set Calibration mode to Manual.
    3. Click Advanced to set the calibration policy and sensitivity. See Table 10-11 for description of the parameters.

      6f16040f160c4d60a573907a113378a3

      Table 10-11  Calibration policy and sensitivity descriptions

      Item

      Description

      Prevent rogue-ap

      Set the radio calibration policy to Prevent rogue-ap.

      When rogue APs (rogue APs cannot be controlled by an AC) exist on a network, set the radio calibration policy to Prevent rogue-ap. The device then implements radio calibration to minimize the rogue AP interference on the entire network.

      Prevent load ap

      Set the radio calibration policy to Prevent load ap.

      When an AP is heavily loaded, set the radio calibration policy to Prevent load ap. The device then preferentially allocates channels with a little interference to the heavily loaded APs.

      Prevent non-wifi

      Set the radio calibration policy to Prevent non-wifi.

      When non-Wi-Fi devices exist on a network, set the radio calibration policy to Prevent non-wifi. The device then implements radio calibration to reduce interference of non-Wi-Fi devices on the network.

      Calibration sensitivity

      Configure radio calibration sensitivity.

      There are three levels of radio calibration sensitivity:
      • Low
      • Medium
      • High

      2.4G calibrate channel set

      5G calibrate channel set

      Configure the global calibration channel set. There are calibration channel sets for 2.4 GHz and 5 GHz radios.

      You can specify a calibration channel set for the AP. When implementing radio calibration, the device can select channels from the calibration channel set. This reduces the burden on the device. There are global calibration channel set and region calibration channel set.

      The device implements radio calibration according to the following principles:
      • If no country code is configured in the AP region, the device implements radio calibration on global calibration channels.
      • If a country code is configured in the AP region, the device implements radio calibration based on whether calibration channels are specified in the AP region.
        • If calibration channels are specified in the AP region, the device implements radio calibration only on channels specified in the AP region.
        • If no calibration channel is specified in the AP region, the device implements radio calibration on channels in the calibration channel set that corresponds to the country code in the AP region.
        • For configurations about the region calibration channel set, see Configuring a Calibration Channel Set in the AP Regionin 10.2.2 AP Region.

    4. Click Apply. The configuration is complete.
    5. Click Start. Manual radio calibration is triggered.
  • Configure automatic calibration.
    1. Click Device Management > AP Maintenance > Radio Calibration. The Radio Calibration page is displayed.
    2. In Radio Calibration Setting, set Calibration mode to Auto and specify the value of Calibration interval.


      458793c1c90a4c29a7dd8baf27f620e4

    3. Click Advanced to set the calibration policy and sensitivity. See Table 10-12 for description of the parameters.

      6f16040f160c4d60a573907a113378a3

      Table 10-12  Calibration policy and sensitivity descriptions

      Item

      Description

      Prevent rogue-ap

      Set the radio calibration policy to Prevent rogue-ap.

      When rogue APs (rogue APs cannot be controlled by an AC) exist on a network, set the radio calibration policy to Prevent rogue-ap. The device then implements radio calibration to minimize the rogue AP interference on the entire network.

      Prevent load ap

      Set the radio calibration policy to Prevent load ap.

      When an AP is heavily loaded, set the radio calibration policy to Prevent load ap. The device then preferentially allocates channels with a little interference to the heavily loaded APs.

      Prevent non-wifi

      Set the radio calibration policy to Prevent non-wifi.

      When non-Wi-Fi devices exist on a network, set the radio calibration policy to Prevent non-wifi. The device then implements radio calibration to reduce interference of non-Wi-Fi devices on the network.

      Calibration sensitivity

      Configure radio calibration sensitivity.

      There are three levels of radio calibration sensitivity:
      • Low
      • Medium
      • High

      2.4G calibrate channel set

      5G calibrate channel set

      Configure the global calibration channel set. There are calibration channel sets for 2.4 GHz and 5 GHz radios.

      You can specify a calibration channel set for the AP. When implementing radio calibration, the device can select channels from the calibration channel set. This reduces the burden on the device. There are global calibration channel set and region calibration channel set.

      The device implements radio calibration according to the following principles:
      • If no country code is configured in the AP region, the device implements radio calibration on global calibration channels.
      • If a country code is configured in the AP region, the device implements radio calibration based on whether calibration channels are specified in the AP region.
        • If calibration channels are specified in the AP region, the device implements radio calibration only on channels specified in the AP region.
        • If no calibration channel is specified in the AP region, the device implements radio calibration on channels in the calibration channel set that corresponds to the country code in the AP region.
        • For configurations about the region calibration channel set, see Configuring a Calibration Channel Set in the AP Regionin 10.2.2 AP Region.

    4. Click Apply. The configuration is complete.
  • Configure scheduled calibration.
    1. Click Device Management > AP Maintenance > Radio Calibration. The Radio Calibration page is displayed.
    2. In Radio Calibration Setting, set Calibration mode to Periodic and specify the value of Calibration time.


      ebc2676b0da64e42965b79d16f4964ea

    3. Click Advanced to set the calibration policy and sensitivity. See Table 10-13 for description of the parameters.

      6f16040f160c4d60a573907a113378a3

      Table 10-13  Calibration policy and sensitivity descriptions

      Item

      Description

      Prevent rogue-ap

      Set the radio calibration policy to Prevent rogue-ap.

      When rogue APs (rogue APs cannot be controlled by an AC) exist on a network, set the radio calibration policy to Prevent rogue-ap. The device then implements radio calibration to minimize the rogue AP interference on the entire network.

      Prevent load ap

      Set the radio calibration policy to Prevent load ap.

      When an AP is heavily loaded, set the radio calibration policy to Prevent load ap. The device then preferentially allocates channels with a little interference to the heavily loaded APs.

      Prevent non-wifi

      Set the radio calibration policy to Prevent non-wifi.

      When non-Wi-Fi devices exist on a network, set the radio calibration policy to Prevent non-wifi. The device then implements radio calibration to reduce interference of non-Wi-Fi devices on the network.

      Calibration sensitivity

      Configure radio calibration sensitivity.

      There are three levels of radio calibration sensitivity:
      • Low
      • Medium
      • High

      2.4G calibrate channel set

      5G calibrate channel set

      Configure the global calibration channel set. There are calibration channel sets for 2.4 GHz and 5 GHz radios.

      You can specify a calibration channel set for the AP. When implementing radio calibration, the device can select channels from the calibration channel set. This reduces the burden on the device. There are global calibration channel set and region calibration channel set.

      The device implements radio calibration according to the following principles:
      • If no country code is configured in the AP region, the device implements radio calibration on global calibration channels.
      • If a country code is configured in the AP region, the device implements radio calibration based on whether calibration channels are specified in the AP region.
        • If calibration channels are specified in the AP region, the device implements radio calibration only on channels specified in the AP region.
        • If no calibration channel is specified in the AP region, the device implements radio calibration on channels in the calibration channel set that corresponds to the country code in the AP region.
        • For configurations about the region calibration channel set, see Configuring a Calibration Channel Set in the AP Regionin 10.2.2 AP Region.

    4. Click Apply. The configuration is complete.
  • Check the calibration result.
    1. Click Device Management > AP Maintenance > Radio Calibration. The Radio Calibration page is displayed.
    2. Click Real-Time Channel And Power List to check the current working channel and power of the radio.


      a36d78e9413a476e8359bd1e06153f38

    3. Set search criteria in Search and click Go. Channel and power of the APs matching the search conditions are displayed. You can check the channel and power of specified APs.

10.4  Backup Configuration

10.4.1  Backup Configuration

Context

In the AC + Fit AP networking, the AC manages and controls WLAN services of users. An AC may control hundreds of APs and thousands of STAs; therefore, the AC must be highly reliable. If the AC is faulty, the services of all users connected to the AC are interrupted. An AC can perform dual-link cold backup, dual-link hot backup, or VRRP hot backup based on actual requirements.
  • Dual-Link Cold Backup

    As shown in Figure 10-7, an active AC and a standby AC are deployed on the WLAN. The AP establishes CAPWAP tunnels with the two ACs, and periodically exchanges CAPWAP packets with the ACs to monitor link status. The active AC controls access of STAs. If the AP detects a fault on the link between the AP and active AC, the AP requests the standby AC to trigger an active/standby switchover, that is, the standby AC becomes the active AC to control access of STAs. This mechanism improves WLAN reliability. After the original active AC is restored, the AP requests the active and standby ACs to perform revertive switchover. The restored AC becomes the active AC again.

    Figure 10-7  Dual-link cold backup networking diagram 
    1711d1954b094af6af413cbe04c286e8
  • Dual-Link Hot Backup

    An AP establishes CAPWAP tunnels with the active AC and standby AC. The two ACs synchronize control information and implement the heartbeat mechanism through the hot standby (HSB) function. When a fault occurs on the active AC, the standby AC can immediately detect it and fast switch the standby CAPWAP tunnel as the new active CAPWAP tunnel to prevent user services from being interrupted.

    Figure 10-8  Dual-link hot backup networking diagram 
    2aa563e6c4f1406b84869c519599e788
  • VRRP Hot Backup

    An AP can only obtain the IP address of one AC, which is the virtual IP address of the active and standby ACs in the VRRP group. The active and standby ACs are elected among the ACs in the VRRP group based on their priorities. The active AC manages and controls all APs and users, and periodically sends the standby AC the status information and information that needs to be backed up, including AP entries, CAPWAP link information, and user information. When a fault occurs on the active AC, the standby AC can immediately detect it using VRRP and fast switch the standby AC as the new active AC to prevent user services from being interrupted.

    Figure 10-9  VRRP hot backup networking diagram 
    e1a50f558daf4146bf998c3741e4c1c8

Procedure

  • Configuring device backup
    1. Log in to the web platform and choose Device Management > Backup Configuration > Backup Configuration. The Backup Configuration page is displayed, as shown Figure 10-10.

      Figure 10-10  Backup Configuration 
      6b8988b820fb4b05805715d3afe26e1d

    2. Select Dual-link cold backup, Dual-link hot backup, or VRRP hot backup according to service requirements, as shown in Figure 10-11, Figure 10-12, and Figure 10-13. Set or enter corresponding backup parameters. For description of the parameters, see Table 10-14, Table 10-15, and Table 10-16.
    3. Click Apply to complete the backup configuration.

      Figure 10-11  Dual-link cold backup 
      06c373add89a4305a109169e3bffb702
      Table 10-14  Description of dual-link cold backup parameters

      Parameter

      Description

      AC dual-link backup state

      Whether to enable dual-link backup. By default, dual-link backup is disabled globally.

      AC dual-link restore state

      Whether to enable the active/standby link switchback function. By default, the active/standby link switchback function is enabled.

      Assume that AC1 is the active AC and AC2 is the backup AC. When the link between AC1 and an AP fails, AC2 takes the active role and the link between AC2 and the AP becomes the active link. In the case that active/standby link switchback is enabled, when the link between AC1 and the AP recovers, the AP detects that AC1 priority is higher than AC2 and instructs AC1 and AC2 to perform switchback. AC1 becomes the active AC again.

      Local priority

      Priority of the AC.

      In dual-link backup mode, the AC with a higher priority acts as the active AC and the AC with a lower priority acts as the standby AC. A smaller value indicates a higher priority.

      Standby AC IP address

      IP address of the standby AC.

      Figure 10-12  Dual-link hot backup 
      719f5a287ea141999ef54b531d524198
      Table 10-15  Description of dual-link hot backup parameters

      Parameter

      Description

      AC dual-link backup state

      For description of this parameter, see Table 10-14.

      AC dual-link restore state

      For description of this parameter, see Table 10-14.

      Local priority

      For description of this parameter, see Table 10-14.

      Standby AC IP address

      For description of this parameter, see Table 10-14.

      HSB channel

      HSB channel. You need to create or modify the HSB channel on the HSB page.

      Backup service

      • User: enables or disables backup of user access services.
      • AP: enables or disables backup of WLAN services.
      Figure 10-13  VRRP hot backup 
      b730bafb02bf4cb79196d91c20d9dc63
      Table 10-16  Description of VRRP hot backup parameters

      Parameter

      Description

      HSB function

      Whether to enable the HSB function. To configure VRRP hot backup, the HSB function must be enabled.

      VRRP version

      VRRP has two versions: Version2 and Version3.

      VRRPv3 does not support authentication, whereas VRRPv2 supports.

      VRRPv3 uses the centiseconds, whereas VRRPv2 uses the seconds.

      Learning the interval for VRRP packets

      Whether to enable the function that learns the interval for sending VRRP packets.

      When the VRRP group switches to the active status due to a link failure, the forwarding of service traffic will be interrupted. Therefore, VRRP smooth switching must be enabled. Before that, you must enable the function that learns the interval for sending VRRP advertisement packets. After this function is enabled, the non-master devices learn the interval for sending VRRP advertisement packets and synchronize their timers with the master device.

      Sending gratuitous ARP packets

      Whether to enable the function that sends gratuitous ARP packets.

      To enable the network elements connected to the AC to learn the virtual IP address of the VRRP group, the VRRP group needs to send gratuitous ARP packets to the network elements.

      Interval for sending gratuitous ARP packets (s)

      Interval for sending gratuitous ARP packets.

      HSB group

      HSB group. You need to create or modify an HSB group on the HSB page.

      Recover delay time(s)

      Specifies the delay in recovering a VRRP group.

10.4.2  VRRP

Context

The Virtual Router Redundancy Protocol (VRRP) integrates multiple routing devices to a virtual router and uses a certain mechanism to switch traffic to a standby router when the next hop router of the host fails, ensuring continuous and reliable communication.

Procedure

  • Creating a VRRP
    1. Log in to the web platform and choose Device Management > Backup Configuration > VRRP. The VRRP configuration page is displayed, as shown in Figure 10-14.

      Figure 10-14  VRRP 
      584f554ba2604be69d878716c4d86fee

    2. Click Create. In the displayed Create VRRP text box, select or enter each parameter for VRRP configuration. For description of the parameters, see Table 10-17.

      be2c94038fa345f494d6408b2b4dec03

    3. Click OK to complete VRRP configuration.

      Table 10-17  Description of the parameters for creating a VRRP group

      Parameter

      Description

      VLANIF/IP

      VLANIF interface that requires VRRP configuration. The VLANIF interface must exist in the system.

      VRID

      ID of a VRRP group. The value range is 1-255.

      Virtual IP

      Virtual IP address of the VRRP group. The virtual IP address can be either an idle IP address in the network segment of the VRRP group or the IP address of an interface in the VRRP group.

      VRRP type

      VRRP group type. Two types of VRRP groups are available: common VRRP group and management VRRP group.

      VRID

      Specifies the VRID of a VRRP group.

      VRRP interface

      Specifies the type and number of the interface configured with an mVRRP group.

      Preemption mode

      Whether to enable the preempt mode. In preempt mode, once a backup device has a higher priority than the current master device, it will automatically take the role as a master device.

      Preemption delay

      Preempt delay time set for the VRRP group.

      By default, the preempt delay time is 0, indicating immediate preemption. A backup device working in immediate preempt mode preempts to be the master device immediately when it detects that its priority is higher than the priority of the current master device.

      Authentication mode

      Available authentication modes for VRRP:
      • None: The device neither authenticates VRRP advertisement packets to be sent nor authenticates received VRRP packets. It considers all the received VRRP packets as valid.

      • MD5: The device uses the Message Digest 5 (MD5) algorithm to encrypt the authentication key and encapsulates the key in an outgoing VRRP advertisement packet. The device that receives the VRRP advertisement packet matches the authentication mode in the packet with the decrypted authentication key to check the validity of the packet.

      • Simple: The device encapsulates the authentication mode and authentication key into an outgoing VRRP advertisement packet. The device that receives the VRRP advertisement packet compares the authentication mode and authentication key in the packet with those configured on itself.

      NOTE:

      MD5 authentication ensures higher security than simple authentication.

      VRRP authentication key

      VRRP authentication modes key.

      Advertisement duration

      Interval (in seconds) for sending VRRP advertisement packets by devices in the VRRP group. For VRRP version2, the value range is 1-255; for VRRP version3, the value range is 1-40.

      The master device sends VRRP advertisement packets to backup devices at intervals to notify the backup devices that it works normally. If backup devices do not receive any VRRP advertisement packets after the timer expires, the backup device with the highest priority becomes the new master device.

      Priority

      Priority of a device in the VRRP group, based on which the device role is determined.

      Monitored Interface
      NOTE:
      The monitored interface is configured only when the VRRP type is set to a management VRRP group.

      Interface name

      Interface that needs to be tracked by VRRP.

      Priority

      Whether to increase or reduce the VRRP priority of the interface to be monitored when the interface is Down.

  • Modifying the VRRP group
    1. Log in to the web platform and choose Device Management > Backup Configuration > VRRP. The VRRP configuration page is displayed, as shown in Figure 10-14.
    2. On the VRRP page, select the VRRP to be modified and click 03308b93a6c8407da26ea5ad46a026c1 on the right.

      ca943d39091143f287b88848320b1701

    3. On the Modify VRRP page, select the VRRP parameters to be modified and enter or select each parameter. For description of the parameters, see Table 10-17.
    4. Click OK to complete VRRP modification.
  • Deleting the VRRP group
    1. Log in to the web platform and choose Device Management > Backup Configuration > VRRP. The VRRP configuration page is displayed, as shown in Figure 10-14.
    2. On the VRRP page, select the check box next to the VRRP to be deleted and click Delete.
    3. In the dialog box that is displayed, click OK. The VRRP is deleted.
  • Searching for VRRP groups
    1. Log in to the web platform and choose Device Management > Backup Configuration > VRRP. The VRRP configuration page is displayed, as shown in Figure 10-14.
    2. In the VRRP area, set the search criteria and click Search. All VRRP groups matching the set conditions are displayed.

10.4.3  HSB

Context

In hot-standby backup mode, there are two devices, one acting as a master device and the other a backup one. The master device forwards services and the backup device monitors the forwarding. The master device periodically sends the backup device the status information and information that needs to be backed up.

To reduce impact of single-point failures on a wireless access network, a traditional backup solution deploys two devices on an access node for backup. Access devices on a wireless network usually run Dynamic Host Configuration Protocol (DHCP), network admission control (NAC), and wireless local area network (WLAN) services, which require real-time information backup from the master device to the backup device. For example, the master DHCP device must synchronize user status information to the backup DHCP device in real time. Otherwise, services will be interrupted after link switching.

Hot Standby (HSB) can implement redundancy between access devices while ensuring uninterrupted service transmission. The HSB service supports batch backup and real-time backup between the two access devices. Before link switching, the backup device synchronizes information from the master device. When the master device fails, service traffic is immediately switched to the backup device without interrupting services. This improves connection availability.

Procedure

  • HSB Channel List

    • Creating an HSB channel

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.

      Figure 10-15  HSB 
      3cc9b943f8574bd68c576b8d138f083f

    2. On the Channel List page, click Create. In Create HSB Channel, select or enter each parameter to configure an HSB channel. For description of the parameters, see Table 10-18.

      3efab6c6fdfb444e9e53d660b3b6fc01

    3. Click OK to complete HSB channel configuration.

      Table 10-18  Description of the parameters for creating an HSB channel

      Parameter

      Description

      Channel ID

      HSB channel ID.

      Local IP

      Local IP address on the HSB channel.

      Peer IP

      Peer IP address on the HSB channel.

      Local port

      Local port on the HSB channel.

      Peer port

      Peer port on the HSB channel.

      Retransmission count

      Number of times for retransmitting heartbeat packets.

      Retransmission interval(s)

      Interval for sending heartbeat packets through the HSB channel.

      Heartbeat packets are used to detect the status of the data synchronization channel in a hot standby group. If the local end does not receive heartbeat packets of the peer end in the interval specified by Retransmit Times*Retransmit Interval, the local end considers that the channel where dual-system HSB data is synchronized is faulty.

    • Modifying an HSB channel

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. On the Channel List page, select the HSB channel to be modified and click 03308b93a6c8407da26ea5ad46a026c1 on the right.

      b9310566b89b4e1a9574637d4cc375de

    3. On the Modify HSB Channel page, choose the HSB channel parameters to be modified and enter or select each parameter. For description of the parameters, see Table 10-18.
    4. Click OK to complete HSB channel modification.

    • Deleting an HSB channel

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. On the Channel List page, select the check box next to the HSB channel to be deleted and click Delete.
    3. In the dialog box that is displayed, click OK. The HSB channel is deleted.

    • Searching for HSB channels

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. In the Channel List area, set the search criteria and click Search. All HSB channels matching the set conditions are displayed.
  • HSB Group

    • Creating an HSB group

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. On the Group List page, click Create. In Create HSB Group, select or enter each parameter to configure an HSB group. For description of the parameters, see Table 10-19.

      6a6b28dd31a241628b62486b6caead89

    3. Click OK to complete HSB group configuration.

      Table 10-19  Description of the parameters for creating an HSB group

      Parameter

      Description

      Group ID

      HSB group ID.

      HSB channel

      HSB channel that has been created.

      Backup service

      • DHCP: enables or disables backup of DHCP services.
      • User: enables or disables backup of user access services.
      • AP: enables or disables backup of WLAN services.

      VRID

      VRRP group ID.

      Interface name

      Interface configured with a VRRP group.

    • Modifying an HSB group

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. On the Group List page, select the HSB group to be modified and click 03308b93a6c8407da26ea5ad46a026c1 on the right.

      8c1178dd74a44af28a70ca613776c914

    3. On the Modify HSB Group page, choose the HSB group parameters to be modified and enter or select each parameter. For description of the parameters, see Table 10-19.
    4. Click OK to complete HSB group modification.

    • Deleting an HSB group

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. On the Group List page, select the check box next to the HSB channel to be deleted and click Delete.
    3. In the dialog box that is displayed, click OK. The HSB group is deleted.

    • Searching for HSB groups

    1. Log in to the web platform and choose Device Management > Backup Configuration > HSB. The HSB configuration page is displayed, as shown in Figure 10-15.
    2. In the Group List area, set the search criteria and click Search. All HSB groups matching the set conditions are displayed.
From group: WLAN

Huawei Wireless Access Controllers V200R003C00 Web Platform Configuration Guide-Device Management
View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.