Last few day, one user consult us the temperature requirement for E9000 chassis server, now after tidy and summarize them here, and share it with you.



1 Temperature requirements

For E9000 chassis

Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-1


For HMM

Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-2


For compute node

Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-3


For Switch Modules

Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-4


2 Heat Dissipation System

    This section describes the components, heat dissipation performance, and fan module installation slots of the E9000 heat dissipation system

2.1 Introduce of heat Dissipation System
2.1.1 Fan Modules and Heat Dissipation Capability
    The heat dissipation system of the E9000 chassis consists of 14 fan modules. When the E9000 chassis is fully configured with fan modules, the maximum heat dissipation power consumption is as follows:
Compute node slot (35°C or 95°F ambient temperature):
Half-width slot: 900 W
Full-width slot: 1800 W
Compute node slot (40°C or 104°F ambient temperature):
Half-width slot: 700 W
Full-width slot: 1400 W
Switch module slot: 280 W
Management module slot: 80 W
    Figure 3 shows the installation positions and slot numbers of fan modules in the chassis.
2.1.2 Fan Module Zones
The 14 fan modules are divided into three zones. Each fan module contains two fan units. If a fan unit or module fails, heat dissipation is not affected.
Figure 1 shows the fan module zones, which are distinguished by colors.
The pink fan zone dissipates heat for the pink front compute node zones.
The turquoise fan zone dissipates heat for the turquoise front compute node zones.
The orange fan zone dissipates heat for the orange rear module (management modules and switch modules) zones.
    Fan modules in the same zone run at the same speed. The speeds of the fans in the three zones are automatically adjusted so that any differences in speed do not exceed 25%.
Figure 1 Fan module zones
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-5
 
2.1.3 Ventilation Channel
Figure 2 Ventilation channels for front nodes
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-6

 
Figure 3 Ventilation channels for rear modules
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-7

 
2.2 Fan Modules
2.2.1 Function
    The E9000 provides 14 fan modules, which are divided into three zones, with each fan module containing two fan units. Each zone supports N+1 redundancy, ensuring heat dissipation is not affected if a fan unit or module fails. The E9000 chassis uses forced air cooling technology and front-to-rear ventilation channels. This ensures that the air enters the chassis from the front and exits from the rear. The fan modules automatically adjust the fan speed based on the operating temperature of compute nodes in the chassis or the management module adjusts the fan speed.

2.2.2 Appearance
Figure 1 Fan module
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-8


2.2.3 Indicator
Figure 2 Indicator on the fan module
 Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-9


Table 1 Indicator status description
 
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-10

3 Fan Module Control Modes

3.1 Control Modes
Fan modules are controlled in the following three modes:
Start mode
When fan modules are powered on, the default fan speed is 30% and lasts for 3s. When the fan module software is initialized, fan modules enter main control mode or automatic mode based on the communication status.
Automatic mode
Before communicating with the active management module, fan modules automatically adjust the fan speed based on the temperature sensor.
Main control mode
After communicating properly with fan modules, the active management module adjusts the fan speed based on the temperatures of the chassis and components. Fan modules do not adjust the fan speed based on their temperatures in this mode.

3.1.1 Automatic Mode
    The following describes the relationship between the fan speed and temperature (T in Figure 1 Fan speed curve) in automatic mode:
T < 35°C (95°F): The fan speed is 25%.
35°C ≤ T < 65°C (149°F): The fan speed linearly changes between 25% and 100%.
65°C (149°F) ≤ T: The fan speed is 100%.
Figure 1 Fan speed curve
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-11
 
3.1.2 Main Control Mode
    Figure 1 shows the relationship between the fan speed and the air intake vent temperature (T) in main control mode. Other factors that affect the fan speed are not described here, such as board temperature alarms and component temperatures.
T < 25°C (77°F): The fan speed is 25%.
25°C (77°F) ≤ T < 30°C (86°F): The fan speed linearly changes between 25% and 40%.
30°C (86°F) ≤ T < 35°C (95°F): The fan speed linearly changes between 40% and 50%.
35°C (95°F) ≤ T < 45°C (113°F): The fan speed linearly changes between 50% and 80%.
45°C (113°F) ≤ T < 55°C (131°F): The fan speed linearly changes between 80% and 100%.
55°C (131°F) ≤ T: The fan speed is 100%.
Figure 2 Fan speed curve
 Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-12

NOTE:
Possible causes of sudden increases in fan speed are as follows:
Certain fan units in the fan module zone are abnormal.
The management modules fail to obtain the temperature of the air intake vent sensor.
The fan modules fail to communicate with the management modules.
A board temperature alarm is generated or there are high-temperature board components in the fan module zone.

3.2 Fan Module Configuration Guidelines
    This section describes the guidelines for configuring fan modules if a chassis houses different numbers of compute nodes.
    Fan modules in the chassis must have sufficient heat dissipation capabilities to ensure that the compute nodes and the system operate properly.
Figure 1 Slot numbers of fan modules 
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-13

NOTICE:
Configure fan modules based on the following guidelines. Otherwise, compute nodes can power off due to insufficient heat dissipation.
Configure fan modules based on the following guidelines:
If a chassis houses eight or fewer half-width compute nodes or four or fewer full-width compute nodes, install all fan modules except fan modules 5, 6, 11, and 12.
If a chassis houses more than eight half-width compute nodes or more than four full-width compute nodes, install all fan modules.

4 Temperature abnormal monitoring

    There are multiple temperature sensors on E9000 chassis and blade server, which monitor the change of running temperature in real time, once one sensor detects the temperature on one part has exteeded the threshold, it will generate the corresponding alarm on HMM and iBMC webUI.
    When system detect the temperature on CPU has reached the limitation of maximum, it will shutdown system automatically, meanwhile it will generate this alarm on HMM and IBMC.
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-14
Huawei E9000 Chassis Server device Temperature requirement and introduce of heat Dissipation System-2708813-15
 

5 Suggesttion

    Please refer the temperature requirement of E9000 chassis server running environment, strictly ensure the humidity and temperature meet the requirement.


This article contains more resources

You need to log in to download or view. No account? Register

x

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.