How to Troubleshoot Air Conditioners Blowing Moist Air or Condensation of IDS500

Latest reply: Mar 28, 2016 05:26:16 1749 1 0 0 0
How to Troubleshoot Air Conditioners Blowing Moist Air or Condensation of IDS5000?

Symptom
Air conditioners blow moist air or condensation.
Possible Cause
The humidity inside the equipment room is high.
The condensate drip pan is blocked.
The humidifier does not work properly.
The temperature and humidity settings are low.
Procedure
Step 1 Check whether humidity inside the equipment room is within the normal range.

Step 2 Check whether the condensate drip pan is blocked.
If yes, clean it and check whether the fault persists.
− If the fault is rectified, no further action is required.
− If the fault persists, go to Step 3.
If no, go to Step 3.
Step 3 Check the operating status of the humidifier. If the humidifier does not work properly, contact
Huawei technical support.

View more
  • x
  • convention:

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.