Water alarm :
If you have water sensor, you must know the alarm of it has been set by default. So there is no need to do setting onsite again. You can try to test by putting some water on the sensor. Then you will get an alarm on LCD.

AC failure alarm :
The alarm of AC failure has been set by default. So there is no need to do setting onsite again. You can turn off the AC input breaker. Then you will get this alarm on LCD, and TP48200A will switch to battery mode to provide supply for loading.
Rectifier communication failure :
The alarm of rectifier communication has been set by default. So there is no need to do setting onsite again. You can pull out one rectifier, then you will get this alarm on LCD.
Rectifier Failure alarm :
This alarm has been set by default. So there is no need to do setting onsite again. You can pull out one rectifier, block the fan using stick and push back the rectifier. Then you will get this alarm on LCD.
High ambient temperature and threshold for this alarm :
Goto---->Parameters settings—Humiture Sensor--Amb. HT Thres.-- 55 degC(default value). Range: 25~80 degC
Battery high temperature and threshold for this alarm :
Goto---->Parameters settings – Battery---Temp. Prot. Para.--- HT Alarm Thres.-- 50 degC(default value). Range: 25~80 degC
Alarm about the air-conditioned when it failure :
This alarm has been confirmed by default. No need to do setting onsite again