The working temperature of VCN is 0~45 degrees.
Normally, the temperature alarm for VCN is set at 35 degrees.
But sometimes the temperature of VCN is too high for some reason, which leads to the alarm.
If the temperature is too high, please check whether the environment in the machine room is really too high. In addition, please check whether only this server has an alarm.
It is recommended to solve this problem first from the machine room environment. For example, this device is not in the cold air passage, you need to change the location, or add air conditioning and so on.
If you must modify the temperature alarm settings, please follow the steps below.
1. Login to the VCN web interface
Maintenance -> Unified Configuration -> Domains -> Module name (OMU) ->Temperature Report -> Edit -> Save.