How to connect a power meter to SmartLogger1000A

806 0 2 0 0

Background:

 

SmartLogger1000A can be connected to and manage only one power meter that supports the Modbus-RTU.

The SmartLogger1000A can be connected to and manage multiple power meters that support the DL/T645 protocol.

 

Application Notice:

 

A multifunctional power meter consists of the measurement unit and data processing unit. It provides time division and required electricity measurement functions in addition to the active/reactive power measurement. The power meter can also display, store, and output data.


1


Procedure:

 

Connect the power meter in one of the empty RS485 communication port and follow the steps below.

 

1.     Configure the communication and protocol for the port

 

Login to the WebUI as Advanced User:


2


 Select the Settings tabàComm. Param., and choose RS485. On the displayed page, set Protocol to DL/T645/ or Modbus, set the parity and baud rate accordingly with the power meter instruction and Submit


3


The default parity mode is even parity for DL/T645. Set parameters based on the power meter instructions.

According to DL/T645, the default baud rate is 2400 bps. Set Baud rate based on the power meter instructions. SmartLogger1000A supports 1200bps, 2400 bps, 4800 bps, 9600 bps, 19200 bps, and 115200 bps at present.

 

2.     Adding the power meter on the WebUI

 

As Advanced User click the Maintenance tab and choose Device Mgmt. àConnect Device, and click Add Devices. In the displayed dialog box, set Device Type to Power Meter, Comm. protocol to DL/T645 or Modbus RTU, Port number where the meter is connected, and specify Address correctly, as shown in the following figure:


4


Smart Logger 1000 can connect to multiple power meters with DL/T645 protocol. Ensure that the addresses of the power meters are not duplicate.

 

3.     Set-up Power Meter Parameters

 

3.1  Power meter with Modbus RTU protocol

 

As Advanced User choose SettingsàComm. Param. àPower Meter, select the power meter type and Submit:

5


If the power meter is not define by default in the Smart Logger 1000A default list you need to choose Power Meter Type - Other and fill the Signal address, Number of Register, Gain and Data Type accordingly with the meter instruction:

6

3.2  Power meter with DL/T645 protocol

 

If you connect a meter with DL/T645 protocol set the running parameter as below:

From Monitoring menu select the MeteràRunning Param. àset the parameter accordingly with the meter instruction

7


4.     Querying device running information

 

From Monitoring menu select the Power Meter and check the device status and the value that the meter reading are correct:

8





Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.