How to Configuring FTU Using Commands

462 0 0 0 0

Configuring FTU Using Commands

1.1Connect the PC and the FTU

Use a serial cable to connect the PC to the CON port on the FTU as shown below

172347nygulgeh6gnjtytu.png

1.2Login the FTU Using the Serial Port Tool

1.2.1Prerequisites

  • You have obtained the PuTTY.

  • You have connected the PC to the device using a serial cable.

1.2.2Procedure

  1. Step 1Start the PuTTY on the PC.

  2. Step 2SelectSerialforConnection type.

  3. 172404o6hkkz7v86hhxkoq.png

Step 3ChooseSerialfrom the navigation tree on the left. Configuring serial port parameters.

172420bkw33334pbzh3cwu.png

  1. Step 4After setting the parameters, clickOpento open the connection device.

1.3Configure FTU with commands

1.3.1Check current configuration

<iManager>display current-configuration

Check Ethernet/0/0/4 and ecc configuration, if it is inconsistent with the plan, please configure according to the plan.

1.3.2Configuration steps

<iManager>display version
<iManager>system-view

Enter system view, return user view with Ctrl+Z.

[iManager]interface Ethernet 0/0/4
[iManager-Ethernet0/0/4]ip address 129.9.0.127 255.255.0.0--Set IPaccording to the plan

Warning: Ip address change from 10.9.0.1 255.255.0.0 to 129.9.0.127 255.255.0.0 may result in device access incapability. Continue? [Y/N]:Y

[iManager-Ethernet0/0/4]quit

[iManager]ecc

[iManager-ecc]ne-id 9 127--Set extension ID and NE ID according to the plan

Warning: The NE ID will change from subnetID: 9 baseID: 1 to subnetID: 9 baseID: 127 may result in device access incapability. Continue? [Y/N]:Y

The NE ID will take effect in the next startup.

[iManager-ecc]ecc network enable
The ECC configuration will take effect in the next startup.

[iManager-ecc]lan
[iManager-ecc-lan]extecc-mode auto

[iManager-ecc-lan]quit

[iManager-ecc]quit

[iManager]quit
<iManager>save

The current configuration will be written to the device. Continue? [Y/N]:Y

<iManager>reboot

1.3.3Confirm the configuration result

<iManager>ecc-ping 9 30--Try to ping other NE.

Ecc-pinging 0x9001e(#9-30) with 56 bytes of data, press CTRL_C to break:

Reply from 0x9001e(#9-30): bytes=56 Sequence=1 time<0ms TTL=255 CRC OK
Reply from 0x9001e(#9-30): bytes=56 Sequence=1 time<0ms TTL=255 CRC OK
Reply from 0x9001e(#9-30): bytes=56 Sequence=1 time<0ms TTL=255 CRC OK

If connection fails, check the configuration and reconfigure.

This post was last edited by GongXiaochuan at 2018-12-22 09:25.

Comment

You need to log in to comment to the post Login | Register
Comment

Notice: To protect the legitimate rights and interests of you, the community, and third parties, do not release content that may bring legal risks to all parties, including but are not limited to the following:
  • Politically sensitive content
  • Content concerning pornography, gambling, and drug abuse
  • Content that may disclose or infringe upon others ' commercial secrets, intellectual properties, including trade marks, copyrights, and patents, and personal privacy
Do not share your account and password with others. All operations performed using your account will be regarded as your own actions and all consequences arising therefrom will be borne by you. For details, see " User Agreement."

My Followers

Login and enjoy all the member benefits

Login

Block
Are you sure to block this user?
Users on your blacklist cannot comment on your post,cannot mention you, cannot send you private messages.
Reminder
Please bind your phone number to obtain invitation bonus.