Step1: You need have one Muti-meter can measure the voltage up to 1000V ( 1500V for 1500V system) .
Step2: Test the voltage between PV+ to PE (Inverter Grounding point or GND point)
Step3: Test the voltage between PV- to PE (Inverter Grounding point or GND point)
Step4: Test the voltage between PV+ to PV-
if Vpv+to PE + Vpv-to PE =Vpv+ to pv-, there is some point short circuit.
if Vpv+to PE + < 70 and Vpv-to PE < 70 might be normal for the system.
if Vpv+to PE + is more than 200V, the maximum value is equal to Vpv+ to pv- , there might be some point have leakage current.