【Problem Analysis】: From the performance data analysis :

We can see the latency is high after 18:00 every.
Then we found that CPU usage kept very high every day.

So the storage system was running at full load during the daytime. After 18:00, the backup service pressure increased, causing the storage system to enter the overload control read state. Therefore, the LUN I/O response latency was high after 18:00.

DBN-KK-ST-SVC05sent a large pressure to storage all day.
【Root Cause】: The storage system was running at full load during the daytime. After 18:00, the backup service pressure increased, causing the storage system to enter the overload control read state. Therefore, the LUN I/O response latency was high after 18:00.
【Solution Description】: Migrate some services to another storage, or expand the controller of this storage.